I have two switches by the front door. One controls the exterior door light. The other controls a light on a pole by the driveway. I want to replace the two switches with a single timer switch that turns both lights on at dusk and off at some later time.

There is a GFCI outlet in the basement ceiling in the circuit for the driveway light. The poles on the switch for the driveway light are connected only to the hot and neutral wires from a single romex coming into the box.

The switch for the door light does not have a GFCI in its circuit. The door light's neutral is pigtailed with other neutrals coming into the box (but not with anything wire from the romex for the driveway light).

If I replace both switches with a single switch, is it possible to wire it in a way that won't confuse the GFCI and will be safe? This is the timer switch I'm looking at using:

https://images.homedepot-static.com/catalog/pdfImages/c2/c2ab5c03-1093-4112-90f3-65259aa738c8.pdf

This switch requires a neutral, line, load, and ground.

Clarification: 1. The two switches are on separate circuit breakers. 2. Both switches are in the same box. It is a 3-gang with one other switch in it as well. 3. The GFCI outlet cuts power to the driveway light when it triggers.

Here is a picture and some explanation. It is crowded in there, but I have labeled the 5 romex cables that enter the box, and the switches.

enter image description here R1: goes to the driveway light. The driveway light, the GFCI in the basement, and another nearby indoor outlet are all controlled by said GFCI. The neutrals for R2, R3, R4, and R4 are all pigtailed together. R2, R3, R4, and R5 are all on the same breaker.

R2 comes from the basement panel. Its black wire is capped, not connected to anything.

R3 goes to the basement panel, it is on a separate breaker from R1.

R4 goes to the outside door light.

R5 goes to the indoor ceiling light.

R5 is the only W/B/R romex, and the indoor light is wired here as if it is a three-way, but there is only a single switch that controls it. Perhaps this is vestigial. But this switch and light are not involved in my question.

2nd edit:

I understand now why I can't combine the two lights into one switch while they are on two different circuit breakers. That makes sense to me. It sounds like one option would be to move one of the lights onto the other's circuit, but I don't know if that would be possible. The driveway light switch with the GFCI circuit is only connected to the one romex, which I have to assume is the hot coming from the GFCI outlet, and the load going to the light. I don't even have access to the neutral for that at the box with the switch. I'd have to run another wire to this already crowded box. Is my reasoning correct?

3rd edit:

Here's a drawing of the wiring of the GFCI in the basement ceiling:

Crude drawing

Each numbered square is a cable going into the GFCI box.

1: comes from the main panel

2 and 3: One of these goes to the indoor outlet. I have no idea where the other one goes. I mapped out what all the circuit breakers control a few years ago, but I must have missed one thing.

4 and 5: since these are in series, they must be the driveway light and switch for the light. 4 should be the switch, and 5 the light.

One way to go would be to take the front door light off the other circuit and route its cable in series with 4 and 5:

GFCI B --> B Switch W --> B Door light W --> B Driveway Light W --> W GFCI

Maybe this isn't good to run two loads in series? Parallel would be better, but I think the running the wiring for that would be much more difficult. But if doing it in series is dangerous, I don't want to do that.

4th edit, responding to @Harper's comments:

The electrician who put in the driveway lamp also put in the basement ceiling GFCI at the same time, so I have to assume it's required. Of the options Harper presented:
- the deadfront (without an outlet) is probably the most acceptable
- An outlet on the switch plate is not acceptable
- a GFCI breaker could also work

It will be very tight in that box with a deadfront, but maybe this will work. Would the way to implement this be:

  1. Connect cable 4 to 5 in the basement to make a passthrough, so that R1 at the switch box goes directly to the driveway light. Now the switch box only has one breaker circuit coming in. The basement GFCI does go there anymore.
  2. Take the hot and neutral feeding the box and split it so it feeds both the switch going to the inside light (R5) and the input of a new deadfront GFCI in the box.
  3. Output of the deadfront GFCI goes to R1 (driveway light) and R4 (outside door light).

Using a GFCI breaker in the circuit panel would mean a solution similar to the above, except the switch box would be less crowded and everything on that circuit would be on GFCI - this includes 5 lights, 3 outlets and 2 garage door opener motors.

Alternately, if I can find the cable in the basement drop ceiling that goes to the switch box, I can stick a second GFCI outlet there instead of in the switch box or breaker.

8
  • 1
    A bit confusing. Pictures of the inside of the existing switch box would be helpful. But one key question: Are the two lights on the same circuit (breaker)? If they are, then this should be straightforward. If not, then they will need to be rewired so that they are on the same circuit to be on the same timer. Also, for each of the lights with the existing switches, is it power->switch->light? or is it power->light->switch? Either one works, but I think if they are both power->switch->light then the install of the new switch will be simpler. Commented Feb 10, 2019 at 20:07
  • Can you post photos of the insides of the existing boxes? It's possible to do this, but you may need some extra parts... Commented Feb 10, 2019 at 20:50
  • Also, is running wire from the driveway light switch box to the door light switch box an option? Commented Feb 10, 2019 at 20:53
  • Is there anywhere on the top, bottom, or sides of that box that looks like you could knock it out to leave a round opening behind? (A "knockout" or "KO", in electrical parlance, IOW) Commented Feb 11, 2019 at 4:04
  • I'm pretty sure there is space for another cable to enter the box.
    – Jerry
    Commented Feb 11, 2019 at 4:32

2 Answers 2

3

What I see coming into this box makes sense. R1 is an old style switch loop. It is not connected in any way to the rest of the cables in the box, and as such, this installation complies with Code as-is.

Now, we really need to know what is going on in the box at the other end of R1. It may be possible to "flip" the switch loop so its power actually comes from here, and it does not use the other circuit breaker at all. That would provide the wires you need.

Your edit shows that is very possible. Simply join those two whites that now go onto the GFCI LOAD, and the circuit bypasses that box entirely. Effectively, the line R1 goes straight to the lamp, which makes it easy to do what you want.

Then you join R1's white to the bundle of whites, and R1's hot to the output of R4‘s switch.

Now, about GFCI on the lamp leg

First, you may not need it. If the line to the pole is old enough, it predates the GFCI requirement, it is grandfathered.

In any case what requires GFCI is not an outdoor lamp, but a branch wire buried to insufficient depth. Conduit at 18” depth does not need GFCI and nor does direct burial at 24". Nor does rigid or intermediate metal conduit at 6".

Regardless, I can think of five ways to add GFCI.

  • a GFCI+receptacle combo device in the now-spare site ...the usual way you'd think of doing it.
  • a GFCI deadfront in the spare site.
  • a GFCI+switch+single receptacle combo device to replace the switch.
  • a GFCI that is a switch to replace the switch. This effectively uses the "Test" and "Reset" buttons to switch.
  • a GFCI+circuit breaker combo device in the service panel
  • any GFCI device anywhere upstream of this location

enter image description here enter image description here enter image description here enter image description here enter image description here


You're never allowed to mix two different circuits' neutrals. Ever.

That creates a serious safety hazard.

Thing about GFCIs is, they just keep you honest. It was already a violation and a safety hazard whether you have GFCIs or not.

If you are comfortable working inside the panel, pull circuit 1‘s neutral,and shut off circuit 2‘s hot. Everything should be dead. If anything powers up, it is improperly using circuit 1's hot and circuit 2‘s neutral. Then reverse and test again.

If you have any entangled neutrals, untangle them. Any hot wires that interact, their partner neutrals should be together, with nothing else.

12
  • Why shouldn't you interconnect neutrals from two different breakers? Aren't they all connected together at the main circuit panel bus? Is it a question of connecting a circuit with some fault in it to another circuit? If so, why wouldn't this apply to connecting neutrals that are on the same breaker together?
    – Jerry
    Commented Feb 10, 2019 at 22:26
  • 2
    Neutrals aren't directly protected from overloads. Mixed up you could have 2 15a hot circuits returning on one neutral == burn up the wire with 30a. Commented Feb 10, 2019 at 23:00
  • 1
    It also violates the equal-current rule: current going out one wire in a cable must return on another wire inthe same cable, so currents net out to zero and magnetic fields cancel each other out. If power comes out one cable's hot and returns in another cable's neutral, then anything metallic between the cables becomes the core of a transformer. The magnetic fields can also physically move wire, making it vibrate, fatigue, break and start a series arc. Eddy currents are not to be trifled with. Commented Feb 10, 2019 at 23:42
  • He actually could do this by using the timer to control a relay.... Commented Feb 11, 2019 at 4:04
  • @Harper I added a drawing of the GFCI box at the other end of R1
    – Jerry
    Commented Feb 13, 2019 at 6:47
0

I mean, the easiest answer here is two timers, right? Seems like a lot of extra work and worry to rewire something that could be solved by two timers. Even better, make them smart switches and add all kinds of extra control if you want it.

3
  • 2
    But the OP wants one timer and our job is to answer his/her question on how to do it.
    – JACK
    Commented Apr 16, 2021 at 2:40
  • True, @JACK, however we do often suggest alternate solutions. Generally, not 2 years later, but we do. (Think direct burial cable vs wiring in conduit, larger panel than OP is asking about, etc.)
    – FreeMan
    Commented Apr 16, 2021 at 13:56
  • @FreeMan True, but we usually answer the question and then suggest alternative solutions.
    – JACK
    Commented Apr 16, 2021 at 14:50