33

I've got a circuit in the basement carrying a handful of outlets. This circuit has no ground wire. I want to add a couple of outlets and want them to be grounded. I may even want gfci outlets on them in the future. I have no reasonable way of getting a ground wire to the panel but I do have easy access to another circuit that does have a ground wire. Is it acceptable to borrow or share a ground wire between circuits? If not, why not?

Both circuits are 20A with 12 AWG wire.

1

5 Answers 5

31

Yes, in most jurisdictions.


NEC 2014

The 2014 version of NEC has made a change to 250.130(C), which now allows you to connect to the equipment grounding conductor of another branch circuit, as long as it originates from the same enclosure. The new text reads as follows:

National Electrical Code 2014

Article 250 - Grounding and Bonding

VII. Methods of Equipment Grounding

250.130 Equipment Grounding Conductor Connections. Equipment grounding conductor connections at the source of separately derived systems shall be made in accordance with 250.30(A)(1). Equipment grounding conductor connections at service equipment shall be made as indicated in 250.130(A) or (B). For replacement of non–grounding-type receptacles with grounding-type receptacles and for branch-circuit extensions only in existing installations that do not have an equipment grounding conductor in the branch circuit, connections shall be permitted as indicated in 250.130(C).

(C) Nongrounding Receptacle Replacement or Branch Circuit Extensions. The equipment grounding conductor of a grounding-type receptacle or a branch-circuit extension shall be permitted to be connected to any of the following:
(1) Any accessible point on the grounding electrode system as described in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure where the branch circuit for the receptacle or branch circuit originates
(4) To an equipment grounding conductor that is part of another branch circuit that originates from the enclosure where the branch circuit for the receptacle or branch circuit originates
(5) For grounded systems, the grounded service conductor within the service equipment enclosure.
(6) For ungrounded systems, the grounding terminal bar within the service equipment enclosure

So if your area has adopted NEC 2014, you can connect a grounding conductor to the grounding conductor from another branch circuit, as long as both circuits originate from the same panel.


NEC 2011

Depending on what code has been adopted in your area, you may not be able to borrow the grounding conductor from another circuit.

Here is what NEC 2011 has to say about replacing receptacles with no equipment ground.

National Electrical Code 2011

Article 250 - Grounding and Bonding

VII. Methods of Equipment Grounding

250.130 Equipment Grounding Conductor Connections. Equipment grounding conductor connections at the source of separately derived systems shall be made in accordance with 250.30(A)(1). Equipment grounding conductor connections at service equipment shall be made as indicated in 250.130(A) or (B). For replacement of non–grounding-type receptacles with grounding-type receptacles and for branch-circuit extensions only in existing installations that do not have an equipment grounding conductor in the branch circuit, connections shall be permitted as indicated in 250.130(C).

(C) Nongrounding Receptacle Replacement or Branch Circuit Extensions. The equipment grounding conductor of a grounding-type receptacle or a branch-circuit extension shall be permitted to be connected to any of the following:
(1) Any accessible point on the grounding electrode system as described in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure where the branch circuit for the receptacle or branch circuit originates
(4) For grounded systems, the grounded service conductor within the service equipment enclosure.
(5) For ungrounded systems, the grounding terminal bar within the service equipment enclosure

Which means you can add a grounding conductor, but only at or before the service panel.

NOTE:
The grounding electrode system (of which the grounding electrode is a part) does NOT include branch circuit equipment grounding conductors. The grounding electrode system is a collection of conductors used to connect the service equipment to earth, and is typically located at or near the service entrance only.

More from the NEC

National Electrical Code 2011

Article 406 - Receptacles, Cord Connectors, and Attachment Plugs (Caps)

406.4 General Installation Requirements. Receptacle outlets shall be located in branch circuits in accordance with Part III of Article 210. General installation requirements shall be in accordance with 406.4(A) through (F).

(C) Methods of Grounding. The equipment grounding conductor contacts of receptacles and cord connectors shall be grounded by connection to the equipment grounding conductor of the circuit supplying the receptacle or cord connector.

(D) Replacements. Replacement of receptacles shall comply with 406.4(D)(1) through (D)(6) as applicable. Arc-fault circuit-interrupter and ground-fault circuit-interrupter type receptacles shall be installed in a readily accessible location.

(1) Grounding-Type Receptacles. Where a grounding means exists in the receptacle enclosure or an equipment grounding conductor is installed in accordance with 250.130(C), grounding-type receptacles shall be used and shall be connected to the equipment grounding conductor in accordance with 406.4(C) or 250.130(C).

(2) Non–Grounding-Type Receptacles. Where attachment to an equipment grounding conductor does not exist in the receptacle enclosure, the installation shall comply with (D)(2)(a), (D)(2)(b), or (D)(2)(c).

(a) A non–grounding-type receptacle(s) shall be permitted to be replaced with another non–grounding-type receptacle( s).

(b) A non–grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter type of receptacle(s). These receptacles shall be marked “No Equipment Ground.” An equipment grounding conductor shall not be connected from the ground-fault circuit interrupter type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.

(c) A non–grounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Grounding-type receptacles supplied through the ground-fault circuit interrupter shall be marked “GFCI Protected” and “No Equipment Ground.” An equipment grounding conductor shall not be connected between the grounding type receptacles.

(3) Ground-Fault Circuit Interrupters. Ground-fault circuit-interrupter protected receptacles shall be provided where replacements are made at receptacle outlets that are required to be so protected elsewhere in this Code.

(4) Arc-Fault Circuit-Interrupter Protection. Where a receptacle outlet is supplied by a branch circuit that requires arc-fault circuit interrupter protection as specified elsewhere in this Code, a replacement receptacle at this outlet shall be one of the following:
(1) A listed outlet branch circuit type arc-fault circuit interrupter receptacle.
(2) A receptacle protected by a listed outlet branch circuit type arc-fault circuit interrupter type receptacle.
(3) A receptacle protected by a listed combination type arc-fault circuit interrupter type circuit breaker.

(5) Tamper-Resistant Receptacles. Listed tamper resistant receptacles shall be provided where replacements are made at receptacle outlets that are required to be tamper-resistant elsewhere in this Code.

(6) Weather-Resistant Receptacles. Weather-resistant receptacles shall be provided where replacements are made at receptacle outlets that are required to be so protected elsewhere in this Code.

There's a good YouTube video, where Mike Holt explains the options for Replacing two-wire receptacles


Consult your local government and/or a licensed electrician, to determine which version of code is used in your area. Codes do change, and you'll always have to follow the code adopted in your area.

6
  • 2
    Wow. Thank you very much for digging up the code on this. This answers half my question. I guess I can speculate on the "why" half of my question: 1) It's confusing to anyone doing work on the electrical in the future. 2) A ground fault on one circuit may present a hazard to anyone assuming the other circuit is not energized. 3) In the exceptionally rare case there is a ground fault on both circuits simultaneously, the ground wire load capability may be exceeded. -- Am I missing anything?
    – Paul
    Commented Dec 12, 2011 at 16:46
  • Now can you create a ground from an appropriate cold water pipe? For example one that then dives under a slab and otherwise has no deliberate dielectric isolation joint?
    – Bryce
    Commented Jan 22, 2018 at 1:06
  • @Bryce not necessarily. The pipe would have to fit one of the items described in 250.130(C)1-6.
    – Tester101
    Commented Jan 22, 2018 at 2:10
  • 1
    > "as long as both circuits originate from the same panel." Does "panel" here mean breaker box? Commented Mar 7, 2021 at 12:51
  • I'm Canadian so I don't care much about the letter of the NEC, but it's great to know I can bond to the same ground on the same box. I recently spent 2 days feeding a grounded NM to a newly renoed room on the second floor, and there are 2 other circuits up there that are still ungrounded. Now I know I can bond them al together and share that ground and not have to go through that torture two more times! Thanks! Commented May 4, 2021 at 23:59
7

It turns out that between the 2011 NEC (which Tester101 cited) and the 2014 NEC -- the answer to this question changed! Under current (2014) code -- a new point 4 was added under 250.130(C):

(4) An equipment grounding conductor that is part of another branch circuit that originates from the enclosure where the branch circuit for the receptacle or branch circuit originates

So, in practice, you can do this provided the circuit you are tapping the equipment grounding conductor (ground wire) from is fed from the same panel as the branch circuit you are trying to ground. Of course, 250.130(C) itself only applies in existing construction!

2
  • Now can you create a ground from an appropriate cold water pipe? For example one that then dives under a slab and otherwise has no deliberate dielectric isolation joint?
    – Bryce
    Commented Jan 22, 2018 at 1:06
  • @Bryce -- that'd be a grounding electrode, not an equipment grounding conductor -- totally different thing Commented Jan 22, 2018 at 1:09
3

Grounds can be joined between circuits, but as Tester points out in his answer, your situation isn't something NEC would approve of.

GFCI won't know the difference since it's looking for a leakage of current out the hot that doesn't return via the neutral, so how you get grounded (be it the ground wire or the bath tub) doesn't mater.

See also this post neutral/ground connections.

2
  • @Tester101, what does NEC have to say on this?
    – BMitch
    Commented Dec 12, 2011 at 14:28
  • 1
    found it 406.3(c).
    – Tester101
    Commented Dec 12, 2011 at 16:47
0

I would say it would be ok to pick up a ground from, another circuit. As long as both circuits are fed from the same panel and that the panel is properly grounded and the required bond wire and bonding screw is installed thru the neutral bus bar is all complete according to code.

1
  • 1
    Hello, and welcome to Stack Exchange. Thanks for the answer, but I've edited out the large amount of information irrelevant to the original question. Commented Mar 9, 2018 at 11:48
-2

To answer your question you can pigback onto existing Ground Wires with no problems. That is what normally happens in a home.

Whether the building codes in your country permit it is another story.

1
  • 2
    The Code compliance of this is somewhat complex, as explained in Tester's and my answers above. Commented Mar 19, 2015 at 2:00

Your Answer