I have a circuit that has a couple outlets and they used 2 wire no grounds. Can I replaced the wire with 3 wire for the outlets and add new 3 prong outlets. It is a long difficut way back to my panel ground bar to run a ground wire for the two wire power source. I have another 240 circiut used for a 4' baseboard heater near my outlets. The baseboard has 3 wire and is grounded back to the panel. Can I run a green wire from the outlets to the ground wire used in the baseboard heater instead of running a seperate green wire back to the panel for the outlets ? Thanks.
-
Is the system non-metallic (Romex) or armored (BX)?– bibAug 3, 2013 at 16:47
-
2Possible duplicate: diy.stackexchange.com/questions/10602/…– bcworkzAug 3, 2013 at 17:56
-
Ok I have some bx cable with metal boxs ground to the panel. Could i run the ground wire to a metal box?– user14348Aug 4, 2013 at 2:01
-
Please register your account and then merge them so you have access to edit, comment, and accept answers on your own question. Posting multiple responses as answers can result in an automated lock that can prevent others from assisting you.– BMitch ♦Aug 4, 2013 at 2:19
-
1The metallic system only solves the problem if the existing box is already grounded through the armor.– bibAug 4, 2013 at 2:19
2 Answers
I would avoid using the baseboard ground for the outlets since the baseboard is on a different breaker (circuit). Per NEC:
NEC 300.3(B) All conductors of the same circuit, including grounding and bonding conductors shall be contained in the same raceway, cable, or trench.
You can certianly replace the home run and associated branches with 3/12 (20 A) or 3/14 (15 A) depending on the circuit breaker size.
-
All my wiring is 12 ga and on 20 amp breakers. I won't be able to pull new romex back to the service panel for these outlets. There is sheetrock and would require alot of work. Aug 4, 2013 at 15:35
-
I'm wondering what the rationale of this rule is. There's an exception for retrofitting ungrounded circuits that you can use a separate ground though I think that you must tie it to the breaker panel, or elsewhere in the same circuit? Must the same circuit be used so that someone doesn't get confused and remove the ground for the circuit accidentally, or is it some safety issue?– PigrewAug 7, 2013 at 18:23
Replacing the outlets with GFCI outlets would be an alternative solution to running a new feed.
-
1GFCI still needs a ground, and using one from another circuit is still a bad idea. Aug 4, 2013 at 23:55