I want to run five 20A 120V circuits and one 20A 240v circuit from my panel (13 circuit carrying conductors, 6 grounds), through a 25' long conduit in my crawlspace, to a junction box where I then splice those in to romex.
My understanding is that the romex will need be #12. What I'm wondering is what size do the conductors in the conduit need to be?
Is the following thinking correct:
- Using Romex limits the circuit to 60degrees, so using THHN in conduit at 60 degrees means the conductors must be #10
- Using 13 circuit carrying conductors in the conduit means I must derate by 50%, which for THHN would be to use #10 (though this is for 90degrees)
Can I say both of these restrictions are met by using #10's in the conduit? Or do I need to apply 2 on top of 1 and then size to #8's?
Does the size of my conduit matter here beyond fill restrictions (which I just punch in to a calculator online)?
(or is there something else I'm missing entirely)