I have a PTAC AC that blows cold air, but barely cools the room. The landlord is claiming its because the room is the livingroom and its an open to the kitchen and hallway.
I know that the rule of thumb for a functional central AC is a 20 degree F delta between the intake and outtake of the AC unit itself. But the PTAC itself has the intake on the bottom and the outtake in the top of the unit.
Question is, what is the HVAC standard for measuring the deltaT? How far should it be taken from the outtake? Or should it be done right at the intake below the unit?
This is an old unit that had the compressor replaced about a year or two ago. I have noticed that the outtake of air is not uniform, and there are significant gaps with weak air coming out.
AC's outtake is about 26" long and 6" wide. The first 2" to 4" from the left dont output much air, the 6" to 8" after it does, then another weak air outflow for another 7"-9", then again, about 6" (or so) of good air flow out, then the last 2" to 4" dont output much. What could be the issue with that?
- Refrigerant (R22 oz): 28.2
- Voltage: 230
- Cont Mtr AMPS: 0.79
- Cooling BTU/hr: 16,900
- Total cooling Amps: 7.30
- Total Cooling Watts: 1,743
- Compressor LRA: 38.00
- Compressor FLA: 6.20
- Evap. Motor Amps: 0.29
- Heating BTU/hr: 0
- Heating Amps: 0.00
- Heater Mtr Amps: 0.29
Test pressure
- High side: 300 psi
- Low side: 150 psi
Max fuse size: 20 Amp time delay on HACR type circuit breaker