Super recently replaced my wall PTAC after my complaints, but the new one is still unable to cool the room to specified temperature. I've set it to 60 F but it stays at 70 or so indefinitely. Outside weather here in NYC has been 80s-90s.
I think I've ruled out internal issues with blower wheel, filter, compressor, refrigerant, etc. by measuring the CFM and wind temperature using the steps below, but let me know if my reasoning is incorrect:
- Measured air discharge rectangular grille area: 28in * 5in = 140, ~1ft^2
- Measured wind speed from cheap Amazon anemometer: approx averages 400 ft/min
- Estimated high cool CFM: 1ft^2 * 400 ft/min = 400 ft^3/min, which is about manufacturer specs (375 CFM)
- Anaeometer also measures wind temperature which matches the setting (set AC to min 60 degrees F, measures 61-62 F)
Based this, I can rule out any any internal issues (refrigerant, compressor, fan, filter, etc.) right? Also ruling out thermostat issues as room temperature is a 1-2 degrees close to separately measured.
Some specs:
- Super replaced old unit with a rebuilt one,
- Room: Studio Apartment, L-shaped living area, ~300sqft. PTAC and window located bottom of L near corner.
- Old unit: Islandaire EZNY12A2GAS44AA, filter was never cleaned, drain pan filled with muddy water. 1200 BTU, might have been too big for studio.
- New unit: Islandaire EZNY07_29AS44AA, rebuilt, serviced recently for "overload rpl (rp/?)". 7000 BTU, seems more appropriate for room. Receptable number: nema 6-20r socket (208/230 line voltage)
- Specs above found in Islandaire's EZ series engineering manual pdf I found online
Based on what I've found above, can I safely assume that the AC is working as normal, but the reason why my room is still never cooling succesfully to the set temperature likely due to air leakage? Otherwise, are there any factors I still haven't ruled out?