We just got a used electric oven. We had propane, but no longer have access to propane. Currently there is only a standard wall outlet behind the oven.
I realize I need to run a new wire, etc., but am over my head as far as what type of wire, what type of breaker, etc.
The metal panel inside the oven door says:
3 wire 120/208 - 240 volts - 60 Hz AC ONLY
KILOWATTS 208 VOLTS
KILOWATTS 240 VOLTS
WHIRLPOOL
MODEL RE374PXDN 0
I have a double-30 breaker open in the box. Can I use that, or should I get something bigger?
Is the "3 wire 120/208" the description of the wire I need?
I tried looking it up by the model number, but it doesn't appear to exist. Any help greatly appreciatedoven
    There should be a number in front of each "kilowatts". Can you post a photo of the panel?
    – DoxyLover
    May 9, 2015 at 2:53
  • Is it a range (stove top and oven in one free standing unit)?
    – Tester101
    May 9, 2015 at 3:15
  • Sorry for the quality, but i attached a photo. I think I translated the details pretty exactly, but.... let me know if you see anything that you need to know that's not legible and i can try for a better photo.
    – Dave
    May 9, 2015 at 4:11
  • Model is RF374PXDN0. Install guide can be found here. whirlpool.com/digitalassets/MLPDF/…
    – diceless
    May 9, 2015 at 4:26
You'll need:
  • NEMA 14-50 receptacle.
  • 40 ampere double pole breaker
  • Four 8 AWG copper conductors, or four 6 AWG aluminum conductors (Hot, Hot, Neutral, Ground).
It's common for builders to use a 50 ampere breaker and larger conductors, to make sure the circuit can handle any range the owner's might use. But if you're installing the circuit to support a particular device, you may be able to use a smaller circuit.
It's common to use aluminum conductors for range circuits, because it's a bit cheaper when you start using larger conductors. Type SE (service entrance) cables are common for range circuits, as it's often easier to pull a cable than individual conductors.
In layman's terms. Go to the electrical supply shop, or hardware store. Tell them what you're doing, and ask for:
  • A four prong range plug.
  • A four wire range cord.
  • 8/3 with ground NM (nonmetallic) cable (copper).
  • A double pole 40 amp breaker.
  • I looked up NEMA 14-50 receptacle, but it looks like it has 4 holes - my chord only has 3. Is that Okay? We hope to get a new/better electric oven soon-ish, if that makes a difference. I have no idea what the "Four 8 AWG copper conductors" are - is there a layman term for those - search came up empty.
    – Dave
    May 9, 2015 at 17:00
  • I have a length of 10-3 wire long enough to use for this - is that the right kind of wire?
    – Dave
    May 9, 2015 at 17:01
    You're going to have to install a new 4 wire cord on the range, and use the 4 prong receptacle. You'll also need 8/3 with ground copper cable, or four 8 gauge individual copper wires. The 10 on your 10-3 cable, means there are 10 AWG (American Wire Gauge) wires (conductors) in the cable. Which are too small for this application. The 3 on the 10-3 cable, means there are 3 current carrying conductors in the cable.
    – Tester101
    May 9, 2015 at 17:09
    You might want to consider having an Electrician install the circuit for you.
    – Tester101
    May 9, 2015 at 17:11
  • Thanks, @Tester101. It's starting to sound like you're right - I should just hire a professional.
    – Dave
    May 9, 2015 at 20:34
The install guide for the oven lists a 40 amp circuit.
  • Is that this part you're referring to?: "A three-wire or four-wire, single-phase, 120/240-volt, 60-Hz, AC-only, electrical supply (or three-wire or four-wire 120/208-volt if specified on the model/serial rating plate) is required on a separate, 40-ampere circuit, fused on both sides of the line."
    – Dave
    May 9, 2015 at 14:44
  • Does that mean a double-40 breaker (in layman's terms?). Also, what type of wire would I need? Will the wire actually show "120/240-volt, 60-Hz, AC-only"? I thought they said things like "13-2" or ... stuff like that. I assume I'd need 3 wire, since the plug that's on it has 3 prongs, which matches the 3-wire diagram.
    – Dave
    May 9, 2015 at 14:46
  • When it comes to circuits beyond normal outlets I'll let others with more experience answer.
    – diceless
    May 10, 2015 at 3:36
-2
just use romex 8/3 with ground or 8/2 that way you'll have your hot nuetral and ground and itll do 40 amps. Grab a 2pole 40 or a "double 40" as you put it