1

We are trying to install an outside receptacle box. We have one GFCI receptacle and one switch/receptacle combo. We want the combo to be protected by the GFCI. We also want the switch to control the bottom half receptacle of the combo. The power source also feeds lights in an outside building past the box we want to install.

Can this be done?

1 Answer 1

3

GFCI protected switched combo device Equipment grounding wires have been omitted for clarity. Don't forget to properly connect all equipment grounding wires.

  1. Connect the white (grounded, neutral) wire from the feeder to the silver screw on the Line side of the GFCI receptacle.
  2. Connect the black (ungrounded, hot) wire from the feeder to the brass screw on the Line side of the GFCI receptacle.
  3. Connect the white (grounded, neutral) wire from the cable feeding the combo device to the silver screw on the Load side of the GFCI receptacle.
  4. Connect the black (ungrounded, hot) wire from the cable feeding the combo device to the brass screw on the Load side of the GFCI receptacle.
  5. Connect the white (grounded, neutral) wire from the GFCI receptacle to the silver screw on the combo device.
  6. Connect the black (ungrounded, hot) wire from the GFCI receptacle to the black screw on the switch half of the combo device.
  7. Break the tab between the terminals on the combo device.
  8. Connect a jumper (red) from the brass (switched) screw of the combo device to the black screw on the receptacle half of the combo device.
  9. Place a "GFCI Protected outlet" sticker on the combo device, and all downstream protected outlets.

GFCI protected outlet

With this setup the receptacle on the combo device will be controlled by the switch on the combo device, and will also be GFCI protected. In the drawing above, I've also included a pass through GFCI protected feeder. This pass through can be used to power, and protect down stream devices.

2
  • A third wire should be present from the incoming line. A bare copper wire wire should be connected to both the GFCI and the switch/outlet green (ground) terminals.
    – HerrBag
    Commented May 22, 2013 at 16:46
  • @HerrBag Added note. This is a couple labels away from being a completely code compliant installation, as is (see NEC 2011 406.4(D)(2)(b) & (c)).
    – Tester101
    Commented May 22, 2013 at 16:53