Update
BUT I also discovered the microwave/wall oven combo unit requires 40A and I think it’s currently on 30A.
That's not necessarily a problem, because ovens and ranges are weird. A typical cooking element is only at full power right after you turn it on. The moment it reaches operating temperature, it starts cycling on and off at a "duty cycle" to maintain target setting. And you are unlikely to throw on all elements at the same time.
This "duty cycle" is allowed for in provisioning of power to ranges. There's a complex formula in NEC Article 220 (which covers commercial ranges as well as residential, and even covers things like a senior active living community that might have 500 ranges; allowing further favorable derate to allow that not everyone will cook at the exact same time).
So, since your breaker is lower than what you think it ought to be, I'd say don't worry about it. It would only be a problem if your particular cooking style is causing breaker trips, in which case NEC probably allows you to go larger. I wouldn't throw all the burners on at the same time to try to provoke a trip, that's a bit silly and defeats the purpose of the Article 220 favorable derates.
Original
Say what now?
30A breakers are NOT legal for:
- gas ovens
- gas tankless water heaters
- Common receptacles (NEMA 5-15 socket)
- "Common plus" receptacles with T neutral (NEMA 5-20 socket)
- 50A sockets of any kind
- NEMA 10-30 sockets unless only for an electric dryer AND installed prior to 1996
So it sounds like "the last guy" was overloading the circuit, and rather than use electricity responsibly, they replaced the breaker with a larger one, destroying the safety of the circuit.
No, it is not safe to do any of that.
You need to search both legs of the circuit to see what size of wires are being used. If any of it is copper #14 or aluminum #12, you need to use the correct 15A breaker.
If all of it is copper #12 or aluminum #10 or larger, then you can use a 15A or 20A breaker.
If all circuit branches have independent neutral wires all the way back to the panel, you can use single breakers.
If one leg has all 20A wire but the other leg has 15A wire, you can use separate size breakers - however if they are sharing a neutral you need a handle-tie between the breakers.
And then, since "the last guy" was a scary unsafe operator, search the house for any other wiring defects.
If the circuit to the outdoor outlet is indeed 20A wire (#12 copper or #10 aluminum) then you can use a NEMA 5-20 outlet there. Note that outdoor outlets need to be GFCI-protected, but there is more than one way to do that.
Running a bouncy castle without GFCI protection isn't even stupid.