0

I'm wiring a Mr. Steamer SAH6000 that is 120V/240V Single Phase. Do I need two hot wires and a ground only or do I also need a common White wire?

8
  • 2
    Downvoted because this question is answered explicitly and clearly in the product instructions. This forum should not be used as a substitute for reading product documentation. If you have trouble applying the instructions to your situation, or if they are unclear or seem to require more knowledge or experience than you have then ask for help here.
    – jay613
    Commented Jun 23, 2021 at 15:40
  • 2
    Reversed 1 downvote as I saw the 240 on 1 page and the 3 wire plug on another. I did not need to see anything further to know the wiring but not everyone will see everything.
    – Ed Beal
    Commented Jun 23, 2021 at 15:49
  • I’m voting to close this question because the question is addressed in the product literature.
    – isherwood
    Commented Jun 23, 2021 at 16:07
  • Note that 240V residential is still single phase. If you go to three phase, there will be talk of Wye vs. Delta. 240V vs 120V are just the line-to-line vs. line-to-neutral voltages.
    – Ben
    Commented Jun 23, 2021 at 17:05
  • 1
    Much as I see the point of everyone saying RTFM, I find myself with no choice but to agree with Ed Beal. I think the manual was clear, but the area of practice is a bit hard. Commented Jun 23, 2021 at 21:07

4 Answers 4

3

According to the installation manual:

Installation Manual

Wiring diagram

This is a 240V ONLY device not 120V/240V as you have mentioned. As such it takes 3 wires, L1, L2, and GROUND.

I strongly urge you to hire a qualified and licensed electrician for this based on your question.

2
  • I missed that print I did look in the installation materials , must have missed that print. Remember we are a diy site and this is a simple install
    – Ed Beal
    Commented Jun 23, 2021 at 15:43
  • @EdBeal My line of thinking is that if you missed it, most likely so would anyone else. Instructions can be obtuse... that doesn't make people bad. Commented Jun 24, 2021 at 18:09
3

Reading the instructions is mandatory...

NEC 110.3(b). You must install according to the labeling and instructions. "Must" is not a suggestion. In order to comply with the instructions, I trust it is fairly obvious that one needs to read them.

That said, if you are laying a circuit for this appliances, there's nothing wrong with including a neutral also. Other appliances may be able to make good use of it.

That thing is not "common".

Common is like a backplane where all the circuits return power. That is fine when they are milliamp electronics circuits or the "common" is a huge steel vehicle frame.

With AC mains power, we wire both sides of the circuit coming and going. The neutral is the current return and it carries the same amount of current as the hot. Each neutral must carry ONLY current for its partner hot(s), or it will overload.

Thus it is not a "common" at all, and one circuit's hot Must Not use another circuit's neutral.

Neutrals certainly can overload. We don't put breakers on neutral because we shouldn't have to. (That only works if everyone wires circuits correctly).

2
  • @ Harper do you have a neutral on your water heater? The device states 240v there is no neutral in 240v
    – Ed Beal
    Commented Jun 23, 2021 at 22:04
  • @EdBeal I don't claim anyone does. I am saying neutral is neutral, and not "common". Commented Jun 24, 2021 at 16:08
2

According to the product specifications it is 240v so 2 hot and a ground would be needed.

The only electrical I could see other than that was a 3 wire 30 amp plug so that would match with the above that it is 2 hots and a ground.

Don’t forget the GFCI breaker as code requires that now in the us.

4
  • The instructions actually say, "Neutral wire is not required" !
    – jay613
    Commented Jun 23, 2021 at 15:43
  • Did I say a neutral was required? No I said a ground only added GFCI as that is a code requirement now.
    – Ed Beal
    Commented Jun 23, 2021 at 15:46
  • 1
    Ed, I think he was reinforcing your answer for the benefit of the asker.
    – isherwood
    Commented Jun 23, 2021 at 16:06
  • Correct, I wasn't refuting your answer Ed! I just thought it was understated and my point was intended more for OP than you. Because the question says "do I need a white wire" and the manual, which is only 13 pages including all the safety warnings, says "you do not need a white wire". :0
    – jay613
    Commented Jun 23, 2021 at 16:43
2

Sorry to belabor the RTFM angle of the comments with a gratuitous Answer but I just had to add this picture. The Electrical part of the instructions are only half a page, five simple steps. The question is "Do I need two wires and do I need a neutral", and one of the five steps says literally and exactly, you need two wires and you don't need a neutral.

So I just don't get how this question isn't an RTFM poster child.

enter image description here

1
  • 1
    Because it's in the fine print, buried enough that even Ed Beal missed it... Commented Jun 24, 2021 at 16:10