My company builds electrical systems that are sold around the world. When our building was being built, we requested that the electricians put a 240V drop in the lab area with a L6-30R receptacle, the idea being that we could plug in transformers as needed to give us high current 120V or 220V single-phase to test systems designed for one or the other (we normally run our systems off of 2 120V, 30A circuits or a single 220V, 30A circuit from a generator). When I checked the voltage at the outlet, I found 208V phase to phase and 120V phase to ground, so it looks like they connected two phases of our three phase supply to the hot terminals.

Looking at isolation transformers to handle these voltages, I'm seeing 216, 228, and 240V primaries, but no 208V. This leads me to suspect that the wiring we have at the outlet isn't "standard". Can we still use this outlet with an isolation transformer and maybe deal with a slight drop in output voltage? Or does it make more sense to rewire the outlet so we get all three phases from the distribution panel?

3
  • 1
    Not exactly a dup., and I am pretty sure that if I VTC it is instant, so take a look at diy.stackexchange.com/questions/197603/… Basically, as I understand it, getting all 3 phases still won't get you to 240, but 208 is close enough for most purposes. Commented Oct 5, 2021 at 20:09
  • If you really want to properly test "world power" you're going to need a geared motor-generator to make 50hz from 60 hz, or else a 50 hz diesel generator...
    – Ecnerwal
    Commented Oct 6, 2021 at 23:22
  • Yes, we'll have to look into whether that's going to be necessary. We've gone out of the way to make sure that all the equipment connected to mains is universal input and interestingly enough, the 220V countries we've deployed systems to have all been 60Hz as well.
    – vir
    Commented Oct 7, 2021 at 16:08

3 Answers 3

4

Your outlet is wired correctly, or at least not incorrectly.

Whether the electricians understood what was wanted, understood themselves the difference in 208 and 240, or understood that it makes a difference to you whereas for most customers 208 and 240 are functionally equivalent, is up for debate -- but the answer won't solve your problem.

Your situation is that you manufacture (or at least design) devices specified to run at 240 volt and you want to develop and test at precisely that voltage, perhaps with a -5/+10% tolerance or whatever your spec is. So, you've got 120/208Y available and you want to get to 240V. You need a transformer. If you really need 30A that's at least 7.2 KVA transformer (perhaps plus overhead for derating, continuous use, power factor, etc).

In theory there are many ways to get there. You'll have to work with your electrician to figure out what's economical in your situation:

  • 2:1 ratio configured for 120-240 step-up
  • multi-tap transformer taking approximately 208 in and making 240 out (this might be marketed as having a 220/240 primary and multi-tap 180-240 output; consult with the vendor but you can probably use it in reverse)
  • 208 to -120/0/+120, ie center-tapped 240
  • if the service to your building is at a higher voltage, perhaps 480 delta or 277/480Y, you could step down from that service to a center-tapped 240 instead of (alongside) the 120/208Y that exists now.

With no endorsement or recommendation intended, there's an example of a 7.5 KVA 208 to center-tapped 240 from LC Magnetics. It's a 10-inch 110-pound cube, so don't forget to team lift when moving it!

transformer

1
  • Thank you, I'll take a look at those. Now that you mention it, the maintenance hangar next to us has a 3-phase drop that would probably be the easiest to deal with for now.
    – vir
    Commented Oct 6, 2021 at 16:22
3

we requested that the electricians put a 240V drop in the lab area with a L6-30R receptacle... When I checked the voltage at the outlet, I found 208V phase to phase and 120V phase to ground, so it looks like they connected two phases of our three phase supply to the hot terminals.

sigh the electricians should have had a conversation with you about that.

When an electric service is provisioned, you generally get power company's choice of either 120/240V split-phase, or 120/208V 3-phase "wye". This is built into the delivery transformers, and there isn't really anything you can do about it.

It is standard that so-called "240V" outlets -- NEMA 6 and NEMA 14 - are wired with 2 of the hot phases available, giving 240V in split-phase territory, and 208V in 3-phase territory. Most appliances are dual-rated for both voltages. (heat making appliances simply run 25% less heat.)

we normally run our systems off of 2 120V, 30A circuits

That should never, ever be done. No plug-and-socket connections should be used to merge two 120V circuits: these are called "suicide cords" - permitting these in a company is negligence ask your insurance company whether they will pay out for accidents involving them. The unplugged plug is dangerous in all modes and cannot be made safe.

Hard-wiring two 120V/30A circuits off 2 breakers should not be done either. Such a load needs, at the very least, a handle-tie between those breakers. And since it is development/testing equipment, it should be a 2-pole breaker which assures common trip, de-energizing the entire machine if one leg overloads. And for personnel protection it should really be a GFCI. (it is obviously not GFCI if you are feeding from two breakers).

My company builds electrical systems that are sold around the world...... the idea being that we could plug in transformers as needed to give us high current 120V or 220V single-phase to test systems designed for one or the other.

Aside from most countries having 50 Hz power (I don't know if that's concern to your equipment)...

The main thing is that all countries with 220V-240V power (except parts of Brazil and the Philippines) have neutral at the same voltage as safety ground. That means for instance that the Line phase is 230V from neutral, not 120V.

Really, to simulate world 220V-240V power, you should be using a step-up/down transformer, or an isolation transformer in boost mode, to increase your 120V supply up to 220V -- but holding neutral and ground at as-supplied from your panel. Such a configuration will also help the GFCIs in your panel protect your staff.

However if you want 30A @ 230V, you will need to start with 60A @ 120V. There is no such thing as a 60A /120V GFCI, so a 60A/240V GFCI would have to be used, with only one hot leg placed in use (unless you needed to test two rigs at once).

You will find a great deal easier time finding step-up transformers, or 120V/120V isolation transformers that can be configured to boost.

1
  • "That should never, ever be done. No plug-and-socket connections should be used to merge two 120V circuits..." oh no, definitely. We use two identical, completely independent AC circuits that are only connected at the low-voltage DC level where they are designed to be backups to each other. I guess the easiest way would be to first identify a transformer and then have a conversation with the electricians to see how best to hook it up.
    – vir
    Commented Oct 6, 2021 at 16:11
0

It's possible that you have multiple voltage systems in your building, especially if it's an older building. You may have a cross system connection somewhere. Very common. As long as the voltages are in phase with each other it won't cause a short. Sounds like you may have a 240 3 phase delta or singe phase system, as well as a 208Y/120 system. Maybe you should get an electrician to look things over.