I am having electrical issues in my out-building shop. I think I might have an idea of what is wrong, but I want to hear others opinions, and I also want to know the best method of repair. I will try to keep this concise.
When I run tools that have a heavy current draw, the lights will completely go out. Some circuits do not work at all. Here are my observations:
- The shop is fed by a 100A breaker from the house
- When I measure the voltage between the main lugs in the shop sub panel, I get 0 volts
- When I measure the voltage between each leg and ground (or neutral) I get 120 V.
- When I measure the voltage at the load side of the 100A breaker in the house, I get 240 V (this tells me the issue isn't the breaker or house feed)
- I removed the wires from the main lugs in the sub panel, then turned the power on and measured the voltage again.
- Between the main lugs, I got 210 V ( a 30V voltage drop)
- One leg has a good 120V, the other has 90V.
My conclusion is that somewhere between the house and the shop, one leg has excessive resistance and dropping voltage completely when I connect to the sub panel as a load.
Does this make sense?
What is the best way to go about fixing this issue? Is it easy enough run new wire in the conduit? Is this a good idea? Would it be better to dig up the conduit and inspect what exactly went wrong?
UPDATE:
- I measured the voltage on the two lugs (wires attached to lugs) as I switched breakers off. My reading again started at 0 volts
- When I switched a particular 20A double pole breaker off, the voltage went from 0 to 180V
- I continued to switch off breakers. When I hit a 20A single pole breaker, the voltage went up from 180V to 210V. Recall 210V was the voltage I was measuring when I removed the wires from the lugs and measured the voltage between them.
- I turned all the breakers back on and the voltage again went to 0. I then went to my 240V machines and unplugged them. The voltage on the main lugs shot back up to 180 or so Volts.
- The garage door opener on the other side of my shop (single pole, powered by the 120V leg) works fine.
I really am starting to think something is up with the one leg on the way to the shop. Can anyone think of anything else I could try? I still need to clean the connections and see what happens.
UPDATE 2:
-AHA!! @Ed Beal was right on the money. If I swap my breakers around so the problematic ones (single pole) are only on one particular leg (the opposite one they were originally on), they all work fine! I can run my tools no problem, and the lights on the one side of the shop now work.
-If I take single leg measurements again (with the 240V tools unplugged) I get 120V on one leg, and 70V on the other leg. So I am certain now that one leg is bad.
Is the only way to fix this to dig up the conduit? I could just pull new wire through but I am worried the conduit has failed or broken somewhere and the new wire will be in the same peril.