About 2 days ago we noticed that a 20 amp (single pole) circuit breaker was tripped. Ok not a big deal, it's doing it's job. Then I noticed that the breaker was tripping even with a single light on. Then it finally came to an end, I was unable to get the breaker to stay in the "on" position at all it would immediately trip.

At this point I thought ok the breaker was pretty old, had never tripped itself before now it's constantly being tripped. I do have some experience with home electrical systems. I have installed several breakers in existing boxes before when I had a job working HVAC. Anyway I thought that there was a possibility that the breaker had went bad, so off I go to get a replacement.

Now here's where I am getting into my real problems--the wire that was and still needs to be connected to the new breaker to finish the circuit and say yay it's been fixed now and possibly is the main cause of all of the issues has no power!! It is essentially a dead line. I found this out when everything was connected back together and honestly better than it was flip the breaker on and immediate trip!!!

How do I find where the dead wire goes and what are possibilities of why it has zero power coming through it.

6
  • 1
    How did you determine that the wire doesn't have power? It sounds like a short to me, and the breaker is doing its job. What loads are on the circuit?
    – isherwood
    Commented Aug 6, 2020 at 13:32
  • 1
    Can you upload a picture of the panel? Commented Aug 6, 2020 at 14:00
  • 1
    No power in the panel at the breaker? What brand & type breaker there are panel types out there that have issues if the buss was damaged but those are not available at most stores , are you sure you have the breaker properly inserted?
    – Ed Beal
    Commented Aug 6, 2020 at 14:18
  • 3
    Did the old breaker have a TEST button on it? When you changed the breaker, did you find white wires attached to it that didn't make any sense? Commented Aug 6, 2020 at 15:19
  • Good point Harp. I didn't think of that. I'm Just old fashioned I guess. + Commented Aug 6, 2020 at 15:52

1 Answer 1

1

Simply put, you have a true short in the cabling someplace. To solve your problem: First of all be sure you are working with the affected outlets and fixtures and don't accidentally pull something out that is still powered up. Then you should pull out all the affected outlets and fixtures and look for any shorts. If none found, take pictures of each one BEFORE. Then disconnect everything including the connection to the breaker. Be sure that you aren't testing anything live by testing for voltage first. Then start testing with a DMM on the ohm setting. You should have near infinite resistance across the white and black in every case. If you find a short (very little resistance), you should be able to find the "other end" of the cable because there should be another pair with low resistance. Then, hooray, you found the cable with the short. What you do from there depends completely on where that cable runs, hopefully not to difficult a replacement. It would be good though, to identify the cause of the short. It's very unusual for the cable itself to be compromised.

But rodent damage can do it: I had a similar situation in my previous house. Some outlets and lights stopped working and another circuit started tripping breakers with nothing plugged into it. The affected outlets were on a wall shared with an attached garage. So I started pulling off sheetrock and this is what I found! Rodent damage to cabling