I have a run in a 20 year old house that is about half out. about half the outlets and 2 overhead lights won't work.

After some troubleshooting, I took 40' of wire left over from an old job to jump from the last working outlet to what I think is the next, about 10 feet down. So, twisted the Jump wire to the panel/working side and connected to the next outlet. Lights and outlets worked throughout the circuit.

Disconnecting the jump wire and removing the first outlet altogether, I twisted the panel wires with the inside wires - basically just took out the outlet. No voltage measured at the 2nd outlet ends - measured at the wires having disconnected the from the outlet. So, nothing in line but a splice.

My multi-meter is old/analog, and I couldn't 0 the ohms But using the 40' as a baseline, it read "35" Ohms for just the 40 feet of wire.

Disconnected the inside wires from the panel wires, and used the jump wire to test continuity inside + jump wires twisted together. The white was about "70" and the black was very high - about 500. That was on the R1K setting. Anything less than 1K doesn't measure, even probe to probe. So the numbers are probably only useful for relative purposes.

Ran scenarios inside black and outside white connected to panel - 0 V at the other end. Outside black and inside white 120V. Outside and outside 120V of course. Inside and inside 0 V. So, black doesn;t work. Again, jumping the inside wires worked to light up the rest of the line. However, even though O-Black and I-White measured 120V, OBlack and IWhite did not reactivate the rest of the circuit. Just the outside jump.

I don't want to just leave a wire running along the floor and I don't want to tear out the wall to replace the inside wire. Suggestions please.

5
  • Can you provide more information about how the faulty wiring run relates to the structure of the house? Commented Apr 1, 2019 at 3:52
  • Do 240V appliances work, e.g. the water heater, dryer and range? Commented Apr 1, 2019 at 4:55
  • I barely moved a large exit vent and an outlet quit working. I replaced line, took out old. Nothing in old line looked damaged. Tested it on another circuit, worked and then didn't... Just saying sometimes we think too much about these things instead of doing what needs to be done. When something isn't working move on, when you see an obvious (but painful repair) just do it.
    – DMoore
    Commented Apr 1, 2019 at 6:13
  • Key question: You state I have a run in a 20 year old house that is about half out. about half the outlets and 2 overhead lights won't work. My answer is based on "a run" == "a specific circuit" - which gets one sort of troubleshooting, similar (though with better tools and more organized) to what you have been doing. But Harper is suggesting maybe half out means HALF OF EVERYTHING IN THE HOUSE and if that's the case then (a) his answer is 100% on target and (b) you have a serious utility-level safety issue. So please clarify - it is critical to determine the answer. Commented Apr 1, 2019 at 14:19
  • Thanks to everyone. Responded to mannasehkatz's answer below. You may hve a point DMoore.
    – John
    Commented Apr 1, 2019 at 23:05

2 Answers 2

4

I have to stop you.

You're making a huge assumption that the dead outlets and the live ones must be "part of the same circuit", and that there's a wire in the wall between them, and that the wire is broken. That's not what's happening at all.

First, wires breaking in walls is rare. And second, a house - especially a 20-year-old house - is a multitude of circuits, 20, 30 or even 40. It's almost certainly true that the "live" circuit you're splicing from, and the "dead" circuit you're splicing to, are totally different circuits.

Ran scenarios inside black and outside white connected to panel - 0 V at the other end. Outside black and inside white 120V. Outside and outside 120V of course.

Wait. If this was one circuit, how is the "inside" (you say the fed, downline) neutral able to return power back to the panel???? It's disconnected, right? No, if it gave the 120V reading, it must be connected back to the panel. The answer is, it does go back to the main panel because it's a separate circuit with its own homerun back to the panel. Then you say

So, twisted the Jump wire to the panel/working side and connected to the next outlet. Lights and outlets worked throughout the circuit.

Yeah, because you were backfeeding.

You said it yourself: about half your house is dead. About half your house. And your house is many circuits. What causes that, I wonder? Read here about houses have 2 poles of power.

Yeah. All the circuits on one pole are dead.

What's actually happening here is your red pole is dead from the power company. You had no idea what you were doing. What you actually did was connect a hot from a "black" circuit to a hot from a "red" circuit -backfeeding not just that circuit, but the whole "red" bus! Making all of them hot (but in-phase when they're supposed to be out-of-phase, 120V loads don't care). So that dead half of your house lit back up again.

This would fail once you drew more than 15-20A on the red side, because you're backfeeding through 15-20A breakers and they'll trip.

If the power company restored your power, your jumper would be connecting opposite poles, and KABOOM! Dead short, and breakers would trip.

You have too little knowledge. If you want to learn the art, then borrow a book from the library and start reading about home electrical, and then get another, and then hang out here for awhile and read and ask questions. You'll eventually get up to speed. In the meantime, no more playing with electricity, K?

As for half your house being dead, call the power company and report an outage because that's what you have. They'll fix it for free in a few hours typically (or tell you it ain't them, at which point it's electrician time). Remember to roll back all these temporary connections before the power company lights you back up.

0

If I follow your logic & testing, you have basically bypassed a group of receptacles and have the circuit partially working. It sounds to me like the problem is one of the receptacles.

I suspect your receptacles are wired with one set of wires going "in" and one coming "out". They may be using screw terminals for both sets, in which case you are looking for a wire that is either on a loose screw and barely hanging on or a wire that may even be too tight and is partially broken. Or you may have one set of wires using screws and the other set using "backstabs", which are more prone to problems. It is also possible, though less likely, that you have a bad receptacle causing the problem.

More testing should narrow this down - essentially take apart every receptacle and put it back together using screw terminals tightened properly. If you find any bad wire (e.g., cracked, almost falling apart (which can cause high resistance)) then cut off the bad part and strip the end for a fresh connection.

The ideal solution is to make a pigtail connection for every receptacle. Basically use a wire nut for each pair of wires (black in/out or white in/out) and add a third short piece of matching wire (you can strip some Romex and use the black & white wires) to connect to the screw on the receptacle. This has the big advantage that if you ever have to remove a bad receptacle in the future, the rest of the circuit will still work because it won't be using the receptacle as a splice.

I also highly recommend getting a digital multimeter. They don't cost much and are incredibly useful. Even better is to get a Electrical Test Kit like this: enter image description here which gives you a basic multimeter, a non-contact tester and a receptacle tester (or magic 8-ball as Harper refers to them), which together can help troubleshoot a lot of issues much easier than with a multimeter (especially an old analog one) alone.

2
  • 1
    You have correctly interpreted the situation. I also assumed it was the first or second receptacle. To simplify the situation, I now have removed both receptacles conn,ecting with wire nuts the wire inside the wall, no power down the line. Directly connecting the jump wire or spare wire instead, I get power down the line. I don't see and can't find a component between the two receptacles, but that is all I can think of besides wire just suddenly going bad, which I admit is highly unlikely.
    – John
    Commented Apr 1, 2019 at 23:02
  • Wires in houses can take strange paths. I have one circuit in my house that winds around through several rooms on two floors. There are two potential complications: 1 - Wiring is a tree topology. It happens to quite often be a single branch, but it can branch multiple times with no rhyme or reason. So you need to look all over the place, not just "down the wall". 2 - Wiring, even a single branch, can "jump around". It might go across to another room before looping back to the same wall, etc. Commented Apr 1, 2019 at 23:12