I keep hearing about tandem breakers, and how they won't work with 240V loads and how they should never be used for a multi-wire branch circuit. Aside from those issues...

What is a tandem breaker?

enter image description here enter image description here

(note: they can be thrown independently).

1
  • 2
    tandem breakers are usually on the same pole 120v where double pole breakers are 240v. I know it is splitting hairs with wording, but I have been called to a home the dryer did not work after a tandem 30 amp breaker was installed DIY. The drum would turn but no heat because it was only 120v. As far as I know all mfg's call there 240 breakers double pole, and tandem or double stuff are on the same pole. With tandem breakers they Cannot be used with a multi wire branch circuit because that would overload the neutral. A double pole,common trip, or 2 adjacent full sized breakers with handle ties
    – Ed Beal
    Commented Feb 26, 2018 at 15:10

2 Answers 2

74

It starts with spaces in the panel

A service panel has a basic unit I call a space. That's apparent when you look at the "knockouts" on the cover.

Electrical power in North America delivers split-phase power. Meaning there are two "legs" or "poles" - L1 and L2 - both 120V from neutral, and opposite-phased so they add up to 240V.

Pic: X-ray of service panel showing bus-bars alternating rows

Here's an X-ray of a service panel cover. See the trick? The buses are arranged in alternating rows. Every other row is a different pole on both sides. Any single-space breaker gets only one pole and 120V (its circuit also attaches to the neutral bar, not shown) -- but a 2-space breaker has access to both poles and 240V.

A single-space breaker cannot get 240V. That's very important when we get to duplex breakers. Now let's fit some breakers.

Pic: striped for legs with breakers in

On the upper right you see a single breaker. This occupies one space and serves one circuit.

On the upper left, you see a 2-pole breaker: this occupies two spaces, and can access both poles L1 and L2. Both sides will trip together if either side overloads. This is used for 240V loads, or for multi-wire branch circuits (MWBC).

enter image description here

Backside of a 2-pole or quad breaker. Note the 2 clips grabbing 2 different poles.

Duplex and friend

On the lower right is the star of the show: the duplex/tandem breaker. This occupies a single space and can only access a single pole. The sides will not trip together. It cannot power 240V loads, it must not power MWBCs, and it is generally used for two unrelated circuits. The entire point of the duplex is to save space in the box. We often call that a "double-stuff" for obvious reasons, and to emphasize how it's different from a 2-pole.

enter image description here

Back of a duplex breaker. Only one clip to grab one pole.

Lower left is the quad breaker, a 2-pole duplex breaker. Again the purpose is to save space. It's just what it looks like, 2 duplexes, except it can access both poles L1 and L2, and it has handle-ties so the inner pair will trip together on overload. That makes it suitable for a 240V load or MWBC. On this model, the outside pair is also tied together with common trip and can serve 240V loads or MWBC. Or, you can get these breakers with outer breakers independent.

General Electric's Q-line panels take a different approach to the problem, and you will never find a quadplex in Q-line.

No substitute for spaces

Most panels only allow these double-stuff breakers in certain positions. Some only forbid it in their labeling, while others actually key the buses so duplex breakers won't fit. Don't force them.

Nowadays in new or remodel work, most circuits must be GFCI and/or AFCI. Here's the trick: for most panels, GFCI/AFCI breakers are not available in duplex/tandem/double-stuff. This is why you can no longer add circuits by switching to these, and why being low on breaker spaces is kind of a big deal. Which is why many of us recommend quite large panels.

The 12-space panel featured here for illustration is terribly small, more befitting a shed than a house. They are made as large as 60 or even 84 space. Many will say "40 circuits/30 spaces" meaning they can accommodate double-stuff's in 10 spaces, but only have 30 total. Watch out for that.

11
  • 10
    Very nice visuals. A great representation and explanation. Commented Mar 12, 2017 at 13:23
  • 1
    Also worth noting is that the modern standards for panels that ALLOW "tandem" breakers is for them to be "CTL" listed, meaning "Circuit Total Limitation". Per this standard, the bus bars in the panel are designed such that only a FEW of the spaces will allow tandem breakers, which ensures that users don't try to exceed the total number of possible circuits. Older panels, now referred to as "Non-CTL" had no restrictions, but the breakers for them have slightly altered mounting arrangements and will not work on newer CTL panels.
    – JRaef
    Commented Feb 13, 2018 at 22:04
  • 3
    I would fully agree with the exception tandem breakers are usually on the same pole 120v where double pole breakers are for 240v. I know it is splitting hairs with wording, but I have been called to a home the dryer did not work after a tandem 30 amp breaker was installed DIY. The drum would turn but no heat because it was only 120v. As far as I know all mfg's call there 240 breakers double pole, and tandem or double stuff are on the same pole.
    – Ed Beal
    Commented Feb 26, 2018 at 15:01
  • 1
    Can you elaborate on GE's Q-line and what they do differently, or point to some resource that explains it?
    – Moshe Katz
    Commented Oct 31, 2018 at 18:14
  • 1
    @jmichas please tell me you turned off your main breaker when you were backfeeding? If not, you could be powering your entire block, and deliver a very unpleasant (read: possibly lethal) surprise to a lineman working on what they believe to be a de-energized line.
    – Doktor J
    Commented Feb 6, 2020 at 16:57
4

The lowdown is panels are sometimes better compact and squeezed down for minimal space saving features. To achieve this, panel manufacturers use what is called tandem breakers.

Most panels have a maximum allocation for tandem breakers and is abbreviated with a ratio. For example 12/24 ( 12 space / 24 circuits ).