I have seen many air conditioners at ground-level in multiple cities near me that are connected using liquid-tight non-flexible conduit (LFNC) whips.
Example: http://www.southwire.com/products/whip-assemblies-ultra-whip-water-well.htm (Note: this is not an endorsement of the product I selected it as an example because it states: "Commonly used for connecting air conditioners" under applications)
Per 2014 NEC section 356.12(1), LFNC shall not be used where subject to physical damage. As I understand, connecting an air conditioner at ground level on an exterior of a home without any surrounding protection like a fence makes the LFNC very much subject to physical damage (particularly from string trimmers).
Are the installations I have seen in violation of code, or does 2014 NEC section 356.10(1) (listed below) somehow trump 356.12(1)?
356.10 Uses Permitted. LFNC shall be permitted to be used in exposed or concealed locations for the following purposes:
Informational Note: Extreme cold may cause some types of nonmetallic conduits to become brittle and therefore more susceptible to damage from physical contact.
(1) Where flexibility is required for installation, operation, or maintenance.