It seems that it is common practice in HVAC-land to use a LFNC whip to connect air conditioner condensing units to the house wiring. However, as statueuphemism rightly points out, it is eminently conceivable that such a wiring connection would be considered "subject to physical damage" under the NEC from errant weed-whackers, mowers, etal.

Considering that there is no flexible wiring means that is allowed by the NEC for use when subject to physical damage, and the use of flexible wiring means to connect to the motor or appliance itself is a practical requirement for motors and motor-driven appliances due to vibration issues, how is one supposed to make these connections in a Code-compliant manner?

2

As far as I can tell:

  • Ensure the conduit is not subject to physical damage
  • Use liquidtight flexible metal conduit (LFMC) (as opposed to LFNC or LFNMC)

enter image description here

LFNC does seem to be commonly used, probably because it's cheaper, but LFMC is acceptable in this case as well and would stand up better to accidental physical damage.

One of the challenges is even if the electrical line is protected, the refrigerant lines also need to be protected. Commonly they are just two flexible copper lines, one wrapped with foam rubber insulation.


NEC 2011 through 2017:

Article 350

350.12 Uses Not Permitted

LFMC shall not be used as follows:

(1) Where subject to physical damage

350.30 Securing and Supporting

(A) Securely Fastened. LFMC shall be securely fastened in place by and approved means within 300mm (12 in.) of each box, cabinet, conduit body, or other conduit termination and shall be supported and secured at intervals not to exceed 1.4m (4.5 ft).

Exception No. 2: Where flexibility is necessary after installation, lengths from the last point where the raceway is securely fastened shall not exceed the following:

(1) 900 mm (3 ft) for metric designators 16 through 35 (trade sizes 1/2 through 1 1/4)

Article 440 is dedicated to Air-Conditioning and Refrigerating Equipment but doesn't have any mention of physical connection requirements.


As originally stated, the highest chance of damage would come from lawn mowers and trimmers, so the best course of action would be to install the unit in such a way to avoid those things.

This could mean ensuring no grass or weeds grow around the unit by using concrete, gravel or pavers (be sure to use landscape fabric underneath):

enter image description here enter image description here

Or mounting it on the wall, so it's high above the business end of lawn equipment:

enter image description here enter image description here

  • I see where you're going here -- but could you expand on how you'd ensure the conduit doesn't get mower-bumped, weed-whacked, etal? – ThreePhaseEel Mar 28 '17 at 3:42
  • @ThreePhaseEel Was literally just doing that. Interesting question by the way, I think you did hit into a grey area that's not well covered. I just spent almost an hour reading air conditioner forum posts and going through the NEC so thanks for that. :) – gregmac Mar 28 '17 at 3:45
  • kind of surprised to see you not upvoting it then :o – ThreePhaseEel Mar 28 '17 at 4:12
  • You guys... I'll go upvote both of you. – Craig Mar 28 '17 at 14:15

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service, privacy policy and cookie policy

Not the answer you're looking for? Browse other questions tagged or ask your own question.