I recently had my a/c system replaced with a heat pump system (Less than 2 weeks ago). The original was a 2.5-ton a/c. The new system is a 3-ton heat pump. I'm now having all sorts of drainage issues with the air handler and would like to confirm if the installation is incorrect. I don't have experience in HVAC, but after some research I can tell that it was done very poorly. I would like to better communicate the issues to the next crew that I hire to fix the issues.
The home only has 1 giant return duct, on the second floor in the hallway. The air handler is above the return, in the attic - mounted horizontally. A few days after the install, I noticed water dripping out of the return duct from the ceiling. Went up into the attic, and the secondary drain pan was dry. Opened up the air handler and saw that it's flooded with water. I called the installer back, only to have them bandaid the real issues with some slight modifications (explained below).
With the unit running, I stuck my head into the return to watch for water and can see that the blower is sucking up water out of the drain pan, and there are droplets of water that seem to be falling directly onto the blower housing - missing the drain pan.
I noticed the following things when I looked over their work (some of which I'm not sure are valid issues):
- The V-shaped evaporator looks like it's installed backwards or upside-down, but I'm not 100% sure. Most photos I see of this same config, has the pointy end of the evaporator towards the blower motor. Looks like the side door was cut where the drain holes are to accomodate the upside-down evaporator. The diagram in the installation manual is also showing the pointy end of the V towards the blower (see photos).
- The P-trap (or lack of). It looks more like a V-trap (?). I think that this issue along with the backwards evaporator are the main culprits.
- Several of the PVC lines are not cemented, but don't seem to be leaking.
- The secondary drain is piped into the primary drain pvc, shouldn't it run separately?
- No overflow safety switch.
- Their bandaid fix was: to raise the drain pan about 1/4" with some wood spacers, and add a piece of insulation to cover the open gap between the evaporator and the blower. The drain hole on the primary pan that they connected to initially seemed correct (lower hole). But after the band-aid visit, they switched to the higher hole and plugged the lower one... seems strange to me.
Attached are photos of the install. Would appreciate any comments and advice on the above. The P-trap would be a pretty simple fix, but I'm really curious about the potentially backwards evaporator. Should I only focus on fixing the P-trap and not worry about the orientation of the evaporator? Thank you
Model numbers of the equipment for reference (AirTemp 3-ton system): Air Handler: AirTemp B6BMM042K-B Heat Pump: AirTemp VSH1BE4M1SP36K
Air Handler layout: Air flow from left to right in photo (return is on the left).
Update on the situation: I cut out and removed their entire “trap” assembly. I installed a proper p-trap in the lower outlet of the primary drain pan. Then installed a safety switch into the overflow outlet of the primary drain pan. I have not yet replaced the secondary drain pan (it’s very rusted), but when I do, I plan to add a water sensor switch on the pan and wire it in series with the overflow safety switch.
Unfortunately my changes to the P-trap didn’t fix the main issue:
- The blower motor is still sucking water out of the edge of the primary drain pan, and onto the unit bottom insulation… flooding the unit and leaking water into the return vent and onto the ceiling drywall.
- This negative pressure seems to still be preventing drainage while the motor runs.
- I can’t figure out if this caused by the gaps that allow air to bypass the evaporator right near the drain hole area, or if it’s caused by an abnormally high negative pressure. I am running the system with no filter at the moment, to rule that out as being a cause of too high negative pressure.
- The unit bottom insulation is completely soaked. Will it need to be replaced? What material can I replace it with?
Thanks for any further suggestions.