5

I swapping a fixture for cosmetic purposes. The old fixture (installed before I was here) has three indistinguishable clear-wrapped wires and a grounding wire.

The wiring in the ceiling is confusing me a lot - I have a bundle of two black and a red, a bundle of three whites, and another lone black wire: attempt at connecting fixture - light always stays on and ignore the switch

Going off of the solution here, I connected white to white, and then black to the black-and-red bundle, and capped the lone black wire. When I kicked power on, the light always stays on, ignoring the switch.

I'm not sure where to go next. I would try just connecting to the red as the link said, but I'm confused how all of this worked with the previous light fixture, and why the two blacks are bundled with the red. This is my first install, so I want to be sure I don't do anything dangerous.

Appreciate any advice!

EDIT 1: adding a picture of previous fixture wiring as requested for clarity: enter image description here One wire was attached to one of each capped bundle in the previous picture.

EDIT 2 adding picture of full previous fixture and closeup of it's make. full fixture enter image description here

11
  • A light fixture with a cable with black and red and white wires usually is connected to three way switches(two switches control the light). Guessing you did not take a picture before removing the old light to see how it was connected. Picture of the old fixture with wires might help.
    – crip659
    Commented Aug 5, 2021 at 19:19
  • 1
    From instructions, you have two grounds for the old light, that makes more sense. Now just need to figure out why you have a three wire cable in there(one with red wire).
    – crip659
    Commented Aug 5, 2021 at 20:38
  • 1
    My guess, and it needs to be verified, is that the red and single black form a run to the switch. NC voltage tester would verify this if the bundle of B/R is always hot, and the single black is switched hot. Commented Aug 5, 2021 at 20:40
  • 1
    That did it! Indeed, the B/R is always hot and the single black switch hot. Capped the b/r and connected the single to fixture black. Works like a charm! Ay my first successful install! Thanks so much folks! @ChrisCudmore feel free to post an answer so I can accept it as the answer
    – jbbj94
    Commented Aug 5, 2021 at 20:43
  • 1
    See answer... To avoid surprising a future DIYer, I'd turn the power off and swap the red and single black to conform to convention. -- If you still have the box open. Commented Aug 5, 2021 at 20:57

2 Answers 2

6

CAUTION: Verify with a non-contact voltage tester. enter image description here First, look at the wires coming in at the red arrow. This appears to be a pair coming in from the panel, and a second pair, spliced into the box, carrying on to another outlet or light. This is a pretty common scenario. Also, the fact that your incorrectly attached fixture is always on suggests that this is so.

Now look at the yellow arrow. This is a RBW trio. Usually, the black is wired in with the other blacks, down to the switch, and the red comes back as a switched hot.

I believe that the red wire and the single black were swapped at some stage. I think the black should be bundled with the others, and the red should be on its own. (I.E. Convention is that blacks are always hot and red are switched hot for this type of install)

TESTING:
Get a non-contact voltage tester. The black-red bundle should be hot. The red should be hot on one switch position, and no voltage in the other.

Fixing it: If the above tests pass,
Turn the power off at the breaker (and check it!!!)

Separate out the red from the bundle and attach the black to the bundle.
Leave the red as the single wire. (Thus abiding by the convention and not surprising future you.)

Attach the red wire to the fixture black, Attach the fixture white to the white bundle.

2

The old fixture appears to have "three indistinguishable clear-wrapped wires", but in fact there will be some means of discerning the function of each wire on the insulation. Unfortunately this is not as straightforward as simply using colored wires, and this has often led to fixtures being installed incorrectly (note that the light will still work when wired backwards but is an electrocution risk). With that in mind, I would ignore how the old fixture wires were hooked up to the wires in the ceiling box.

You don't need to know this since you are removing the clear-wired fixture, but to be thorough, here is how to differentiate the seemingly identical clear wires: sometimes a wire's insulation will have a slight texture on it and this indicates neutral. Other times there will be a stripe along the length of the wire's insulation and this also indicates neutral. And sometimes the conductors themselves are different colors (copper = hot and silver = neutral), but that is not the case in your example.

You can discern which wires are always hot and which are switched in the ceiling box by using a non-contact voltage tester and testing each individual wire with the switch both on and off. When you find the switched wire, you should connect it to the fixture's black wire.