Search options answers only not deleted user 47125
1 vote
Accepted

How does an inverter use excess solar capacity to charge a DC connected battery?

Plus a separate 5kW inverter... same as if you bought those components as separates. They are in a single enclosure and acting on the same battery. … Your AC output will be capped at 5kW because that's the size of your AC inverter. …
Harper - Reinstate Monica's user avatar
3 votes

Off Grid Solar System - 250 amps of Inverter capacity - What load center do I use?

Option 2: move one inverter to its own panel. Now you're at 187.5 amps give or take, well within the capacity of a resi 200A load center. … Option 3: Conservation > Generation: Get more efficient appliances What's got me puzzled is why an off-grid house needs 250A of inverter. …
Harper - Reinstate Monica's user avatar
3 votes

Interlock for GE PowerMark plus subpanel

They demanded development of a totally new kind of system, called a "grid forming inverter". This thing is MAGIC. … On a grid-forming inverter you definitely don't want to interlock out the solar - you want them feeding the same bus. That inverter, though Nothing easier. …
Harper - Reinstate Monica's user avatar
2 votes

Help understanding grid tie inverters with limiters

At a physical level, can anyone explain how the inverter can provide power at a higher priority than the grid? … I don't understand how it seems that the inverter can supply 95% of the demand overriding the supply of the grid. …
Harper - Reinstate Monica's user avatar
14 votes

Solar-electric system not generating rated power

Given that max is never gonna happen... how do we size the inverter(s)? … Using the max possible inverter capacity limits your array size - if you had used 410-425W inverters, you'd be limited to nine of them. By dropping the inverter to 300W, you can have twelve. …
Harper - Reinstate Monica's user avatar
5 votes

Can micro inverters be fooled to feed back-up when grid is down?

It's called a "Grid Forming Inverter" and it is able to trick the microinverter solar panels into powering up. … So your question is: is a "Grid Forming Inverter" just a cheaply made (but weirdly overpriced for what it is) inverter off Banggood, but with a fancy designer label and price tag? No. It is not. …
Harper - Reinstate Monica's user avatar
6 votes
Accepted

Does an off-grid solar inverter need to be UL listed?

But this is not the inverter you want. You want an off-grid or grid-down inverter, aka "plain old inverter". … Now, let's talk about that inverter and the B word. Once the critical-loads sub is finished, all you need is an off-grid solar inverter that takes power from solar panels. …
Harper - Reinstate Monica's user avatar
3 votes

Solar inverter output protection breaker

A Grid-Tie system should be isolated First, if this is a grid tied system, the inverter should comply with UL 1741 aka IEC 62109 rules for grid following, and totally shut down and isolate when it is not …
Harper - Reinstate Monica's user avatar
1 vote

Can I Still Use 2nd Hot Wire In Panel If I Rewired Panel For 120V?

What you cannot do, for instance, is use a 120V generator to feed black+white, and another 120V generator or solar inverter to feed red+white. …
Harper - Reinstate Monica's user avatar
12 votes

Will higher BTU A/C inverter not work in room that needs 18K BTU?

However that should not be a problem for an inverter heat pump as you say you have. … The inverter drive means it can run at variable speed to suit conditions, and will run on "low" for an extended period, assuring that dehumidification happens normally. …
Harper - Reinstate Monica's user avatar
2 votes

Can an inverter be supplied by a battery with lower AH than required for designed VA?

But what you're overlooking is inverter losses aren't just a percentage, they are also a "flat rate" required to have the inverter "spun up" at all. … Can the inverter be a high 900VA device supplied by low AH batteries E.g. 2 Car batteries rated at 45AH each? The inverter might suffice but the battery sure won't. …
Harper - Reinstate Monica's user avatar
2 votes

Automatic Timer Solar Cutoff

I'm never a fan of "all-in-one" units because you get mediocre everything and you cannot choose the best solar charge controller, battery charger and inverter. …
Harper - Reinstate Monica's user avatar
2 votes

Where would a transformer be installed for a Tesup wind turbine?

We Americans have a word: "Get-there-itis". The disease of focusing on one task to the negligence of safety. The RCD is there to protect your home from fire and its occupants from electric shock. Dow …
Harper - Reinstate Monica's user avatar
2 votes

How do I ground an AC inverter in a RV?

TLDR: Do bond the inverter. Use a "generator interlock" or other DPDT switch that switches both hot and neutral between shore power and inverter. … That "switch" could consist of an outlet (fed from the inverter) right next to the RV's inlet. To run on inverter simply use a 1' extension cord to jumper the outlet to the inlet. …
Harper - Reinstate Monica's user avatar
3 votes

Wiring an inverter into an RV using an contactor (AC Relay)

Into it go two 2-pole breakers: one of them 30A (for the utility side) and the other is probably 15A (or whatever is appropriate for the inverter). … On inverter, the inverter bonds neutral and ground, and this isn't disconnected by a normal switch. So the RV is bonding neutral and ground from the house. …
Harper - Reinstate Monica's user avatar

15 30 50 per page