This is a follow-up to my previous question about a bad neutral. The dimming lights/fluctuating voltage problem mostly went away after the PoCo tightened the neutral connection on my side of the meter 'a few turns.' I still measure some current (.15A-2A) on the ground conductor connected to the copper pipe of the water service entrance. I have another ground conductor in my main panel that is connected to a ufer ground that measures no current. (edit: The conductor outside my house leading to the ground rod also measures no current.)
I turned off the main breaker and put a clamp ammeter on the water service ground wire (edit: and the service entrance neutral) and I'm still getting some current (~.1A). Is there any reason for this? From the pictures, you can see that the current is slightly lower near the water entrance. I'm not sure if that's significant. Is this still a PoCo issue?