I’m going to be installing a 200A meter base with a 200A breaker in it, which acts as an external disconnect (required in California). Here’s the spec sheet for it.
The load center I’m using (model LP422-MB) has a 225A main breaker in it. Here’s the spec sheet for it.
I’m pretty sure that between the load center and the meter base I need 250 MCM aluminum SER cable. Right?
But where I start to get fuzzier is between the meter base and the service drop. The 200A meter is rated for 200A continuous load but something like 250A max load. And the load center is rated for 225A. The amperage for aluminum XHHW is:
- 200A - 4/0
- 250A - 300 MCM
- 225A - 250 MCM
So… which one do I go off of? 😅
Thanks for your help! 🙏🏼