I need to run a feeder cable (3 individual 2/0 Al for HOT/NEU and one 6AWG Cu for ground) from an external main panel to a subpanel inside the house.

The wires need to enter the crawl space before entering the house through bottom plate to reach the subpanel. The external run is being done with 2 inch SCH40 PVC conduit. But as soon as you enter the crawlspace, there are far too many obstructions to do a straight PVC run. Even if I use conduit bodies and junction boxes to get around the 360 degree rule, it's quite complicated.

So my questions is whether I can use liquid tight flexible conduit in the crawlspace. I will properly support it with metal/pvc hanger strapping to the floor joists. But is this transition allowed by the code? It will make my life so much easier if this is code compliant.

If this is indeed allowed, what is the best way to connect the two types of conduits?

8
  • 1
    If the routing is reasonably protected, smurf tube should suffice. aka ENT. You may want that pulling point, though - when flexible conduit is floppy-doppy, pulling forces increase. Commented May 26, 2022 at 5:49
  • 1
    If the 360 rule is a problem for PVC (which is nice and slippery and easy to pull in) it's going to be twice as bad for liquidtight (which is sticky miserable [bleep] to pull in.) You don't get a magical pass on 360 when using that - quite the opposite.
    – Ecnerwal
    Commented May 26, 2022 at 12:18
  • In most cases the external part needs to be Sch 80 for "protection from damage" as in most cases the external part will be considered "exposed to damage" if it's not above 8 feet or buried. All kinds of fun if the inspector shows up after you fought your wires into the Sch 40 and tells you to change the conduit to Sch. 80....
    – Ecnerwal
    Commented May 26, 2022 at 12:24
  • 1
    Can you transition to a cable wiring method at an exterior box? Commented May 26, 2022 at 22:37
  • 1
    @cryptic0 fair enough then Commented May 27, 2022 at 0:46

1 Answer 1

2

You can do this if you use the correct pipe fittings. You cannot just glue the liquid tite into a sch. 40 PVC coupling.

The best connection would be into a large junction box (which you could use as just a pull can).

Otherwise, without the j-box, you would need to get a fitting that is certified for use with the liquid tite and would end in either male or female threads and attach that to either a male or female rigid PVC adapter. This might make you wire pull more difficult- hence the j-box suggestion.