I'm going to be running a new electrical line to a new shed. I opened up my breaker box and came across what's pictured below.

The top 20A breaker goes to our well pump, and the 15A goes to the shed. If I follow the wires, the neutral wire from the well pump (which is the back connection) connects to the 15A shed's breaker. Is that normal?

enter image description here

enter image description here

1
  • 2
    If you turn off the bottom 15A "shed" breaker, does the well quit working? What makes you say the wire is a neutral? Commented Mar 12, 2021 at 21:39

2 Answers 2

20

That's not a neutral, and this is not a correct/compliant/safe installation.

Your well pump is 240V. Cable comes black, white, ground and when you have a 240V only load, the white wire is a second hot. In conduit, you would use a hot color (2 blacks, or black & red, or one of the various other colors) but in cable, 2 conductors is black & white.

It should be "re-marked" with black or red tape or paint or heat-shrink, but it often isn't.

It should NOT be connected to two independent breakers. It should be connected to a dual-pole breaker which will be twice as wide as the single-pole breakers you show, and clip onto TWO of the bus wings.

[want proof? turn off your shed breaker and watch your well pump not run. But you might find power in the shed, to an extent (at least enough to shock you) if the well pump is trying to run, since power will pass through the motor windings (at half-voltage) and then to your shed circuit - this Not Good.]

So, buy a dual-pole breaker of the correct size for your pump, re-mark the white wire with red or black, and connect the well black and re-marked white to the two terminals on the new dual-pole breaker, leaving your shed circuit out of the well circuit.

You'll have a 20A single pole breaker (that you will remove the black pump wire from) to use for whatever new thing you are adding...

Obligatory reminder to use a torque screwdriver or wrench for tightening the terminal screws - values are on the box label, and molded into the breakers themselves (35 in-lb for the breakers, if I recall correctly)

Further issues, responding to comments.

Yes, the neutral being double-stuffed is wrong. Every neutral gets its own hole. Grounds may be able to share, that should be detailed on the panel label that also has the torques for the ground/neutral bar screws.

The well breaker should be a double-pole, probably 15 or 20 amps, size should be specified in the pump's documentation (if you have it or know what it is.) If it's not tripping the 15A shed breaker that feeds half of it, 15A might be sufficient (if documentation is missing.) Looks like you could put that on the bottom and move the shed up - or you can wire-nut an extension onto the well white to make it reach the top position. Breaker panels ARE junction boxes, though there's a common misconception that they are not.

10
  • Just so i understand,,That 20 AMP breaker needs to be swapped out for a bigger dual pole breaker, the black & white wires from the well pump would be connected. Would the new breaker need to be GFCI ? It looks like that "white wire" from the well wouldn't reach that top 20 AMP breaker. It doesn't matter where the breaker goes on that board ,just as long as its wired correctly? And on that Buss bar, it looks like the ground and neutral from the shed power is on the same screw,, that good? I cant believe this has been like this for the last year ,, well damn !
    – Jben04
    Commented Mar 12, 2021 at 20:17
  • 2
    @Jben04 the main violation here is that the two breakers for the well aren't handle-tied. The secondary violation is that the shed just taps one leg of the well breaker, but that is not a violation if the well pump is <7.5 amps. The tertiary violation is the neutral wire on the neutral bar is double-lugged with another wire. Grounds can share lugs - neutrals can't. Commented Mar 12, 2021 at 21:42
  • So that white neutral wire,, each needs its own screw?,, but the Ground wires can share the screws?
    – Jben04
    Commented Mar 12, 2021 at 21:48
  • @Jben04 -- correct. neutrals need their own screw for a couple reasons practically speaking, and are also required to be allocated their own screws by Code Commented Mar 12, 2021 at 23:34
  • @Ecnerwal.. this is the panel; outside the house..( Actually a mobile home),, then we have the box inside the house that has breakers for the kitchen, bedrooms, range, A/C etc. Regarding the breakers ,i can just get the double pole breaker,and move it down and move the shed up correct?.. also is it recommended to use a GFCI breaker?
    – Jben04
    Commented Mar 12, 2021 at 23:48
12

You have a 240V pump misusing black and white as its wire colors and improperly fused.

It's also a weird, but not illegal multi-wire branch circuit... it has 2 trivial defects... it could be fixed, but it's a stupid design so we'll get rid of it.

What you really need to do

First, the length of the "white wire" is a nothingburger. It is too short, yes, but it is trivial to extend it with a pigtail and a wire nut. Go to any hardware store that sells wire by-the-foot and get 1 foot of red #12 THHN wire. (an individual wire). You'll also need a yellow or red wire nut.

Also get a 5-pack of multi-colored electrical tape ($4-5). That white wire should have been marked black or a color to indicate it is a hot. Even though you're extending it, it still must be marked. Mark it red, since that most clearly indicates its function.

They should not have poached/tapped that other breaker like that. Instead of the $5 breaker they used, they should have bought a $10 HOM220 2-pole breaker. It is twice as wide. Install that in place of the breaker now there. The black and white-now-red go to this breaker.

Really, feel free to place any breaker in any position, to match up with whichever panel knockouts have been removed on the cover. If you need to knock one out, just choose carefully.

If you have any empty holes in the cover (because of too many knockouts being busted out), fill them. Stick your old 20A breaker there. If you need more, they're $5.

Lastly, correct the neutral-ground double-tap on the neutral bar. You can only put 1 neutral per screw. If you were crammed for space, you can buy accessory ground bars, or they allow some number (2 or 3) of ground wires to share a screw.

3
  • Thanks for the help from everyone.Ended up moving the double 20 amp (Well) breaker i bought down, and colouring the white wire black.Moved the 15 amp shed up.What i did also notice was that the breaker had a little rust on the side where its joined,, is this normal?
    – Jben04
    Commented Mar 14, 2021 at 13:40
  • 2
    @Jben04 Sounds good, but don't just move the breaker down. Also extend the wire. The wire is currently so short it is pulling the breaker out of position, and that is causing poor contact at the bus stab, and inevitably, arcing and burn-up of that stab. You only have 8, and that's a $500 panel, and it takes 2 power company visits to de-energize it, so don't risk it! Commented Mar 14, 2021 at 16:26
  • Added a photo to my post above.. Think i did ok ?,, as you mentioned i need to extend that white (hot wire) ill get to the store in the morning for what i need. I do have 100FT of 12/2 ground romex on hand, ( for another project) i could strip and use some of its black wire from there? My other concern is that top 15 Amp breaker as you see the nut has rust,, recommend that be replaced?
    – Jben04
    Commented Mar 14, 2021 at 18:12