LG fridge works for a while + then trips. Checked, its not the power supply/plug. Electrician replaced 20A circuit breaker with 25A. Worked for 3 days then tripped again. Works when I use normal 2-core cable to plug in fridge i.e. unearthed. Don’t have LG agency or fridge experts in our small town. Can unearthed connection cause harm? What is the prob? THANKS
1What model is this fridge, and where on Earth are you? Also, does your breaker have a TEST button on it?– ThreePhaseEelCommented Jan 23, 2021 at 6:28
4Would probably get a new electrician first. Most fridges only need a 15 amp circuit. Sounds like maybe a short to ground in fridge or circuit, which can kill you. Adding a bigger breaker to a circuit, tells you have an idiot working for you.– crip659Commented Jan 23, 2021 at 13:56
1 Answer
GET A NEW ELECTRICIAN! Not only is putting a 25a breaker in a code violation at least in the NEC it is probably a real issue. Things like defrost coils go bad think of your heating element on an electric stove this is similar to what may have failed . Increasing the breaker has increased the fire risk! I say this as a licensed Electrician that also has HVAC licenses. Track the cycle of tripping and contact an appliance repair person, some HVAC shops also do repair refrigerators but at a 3 day cycle this is most likely the problem and it will burn open in some cases then your fridge will start icing up or not cooling correctly. Don’t risk a fire get it fixed and get the 20 amp breaker back in place if it is the right size for the wire or possibly 15 amp.
FYI "2-core" suggests the British Empire, and 20/25A sizes suggests Australia/New Zealand locale.The time-of-post tends to agree with that. Commented Jan 23, 2021 at 18:40
2@harper so you are saying this is fine? I have seen 25 amp breakers in the US but my statement stands both on upsizing a breaker and a possible defrost circuit failure no matter where in the world they are.– Ed BealCommented Jan 23, 2021 at 21:09
No, I'm not saying that. I'm implying that you might consider revisiting your answer based on that location. Commented Jan 24, 2021 at 1:36
Thanks for the help. In South Africa electrician rules are few. I will take up the 25 to 20A with them - thanks. They told me the fridge breaker also has many other plug on it like washing machine, kitchen utensils. The model fridge is LG GR389SQF .– PeterCommented Jan 24, 2021 at 10:33
Thanks for the help. In South Africa electrician rules are few. I will take up the 25 to 20A with them - thanks. They told me the fridge breaker also has many other plug on it like washing machine, kitchen utensils. The model fridge is LG GR389SQF . – Peter– PeterCommented Jan 24, 2021 at 10:34