I live in a high rise apartment built in the '70s (USA), and this afternoon we suddenly lost all power to just our unit. After some investigation we found that the main disconnect (70A) powering our unit had tripped. When I looked into our own load center, the oven/range breaker (50A) was also tripped.
We weren't doing anything unusual - the oven was on and some lights, but we've often had the dishwasher/lights/hair dryers/etc. running simultaneously. I find it strange that both the 50A and the 70A tripped simultaneously. Does anyone know why this can happen?
If it's relevant, I have installed some LED light bulbs into dimmers that are not for LEDs (on different circuits from the oven/range circuit) and some of them were on at the time. Doesn't seem like that should be relevant but it's the only thing I can think of.
UPDATE - found the root cause! It turns out the range and the cooktop were combined together in a box in the cupboard with wire nuts and then a single line was run to the 50A breaker. Wires in one of the connections melted the plastic and shorted, tripping the breaker.
Currently we have only the cooktop connected, as there's significant work required to bring the unit up to the current code (last remodel was 10 years ago). They'll have to move the panel outside of the closet and increase the size as all the current spaces are doubled up.
Photo of the carnage - thank you to the poster who told me to keep the breaker shut off!