I have a halogen light fixture that is powered by a three-way switch at the top of the stairs and another three-way switch at the bottom of the stairs. After I replaced both switches with new 3-way switches the light fixture stopped working.

The old switches were connected with black, white, and red wires and I replicated the same connections with the replacement switches. I used a voltage tester and turned off the breaker box switch before touching the wiring.

The light fixture has left and right ends that hold the small halogen light bulb. After several hours of testing the best outcome I can achieve is the right end outputting power but the fixture will no longer power the light bulb.

Here's some info:

Switch 1 Switch 1

  • Located at the top of the stairs
  • Bottom right black screw connected to black wire
  • Top right bronze screw connected to red wire
  • Left bronze screw connected to white wire
  • Green screw connected to ground wire
  • Removed the new switch, turned on the breaker box, and the voltage tester showed only the black wire is hot
  • Tried replacing the new switch with the old one with no success
  • Tried replacing the new switch with a couple other new switches with no success

Switch 2 enter image description here

  • Located at the bottom of the stairs
  • Bottom right black screw connected to black wire
  • Top right bronze screw connected to white wire
  • Left bronze screw connected to red wire
  • Green screw connected to ground wire
  • Both switches turned on shows black, red, and white wires are hot
  • Removed the new switch, turned on the breaker box, and the voltage tester showed none of the wires are hot
  • Tried replacing the new switch with the old one with no success
  • Tried replacing the new switch with a couple other new switches with no success

Light fixture Light fixture

  • Using the above wiring and placing the voltage tester in each end of the bulb bracket shows the right end is hot but the left end is not
  • None of the wiring connections below would power the fixture's bulb
  • Uses a J Type 118mm Double Ended 120 Volts 150 Watt T3 Halogen Bulb
  • Tried two different light bulbs

With this wiring I observed these results (only difference is the switch 2 red wire is hot or not):

  • Switch 1 on and switch 2 on: both sets of black, white, and red wires are hot
  • Switch 1 on and switch 2 off: switch 1 black, white, and red wires are hot and switch 2 black and white wires are hot and the red wire is not
  • Switch 1 off and switch 2 on: both sets of black, white, and red wires are hot
  • Switch 1 off and switch 2 off: switch 1 black, white, and red wires are hot and switch 2 black and white wires are hot and the red wire is not

I tried several different combinations of left and right bronze screws but none would power both ends of the fixture:

  • Switch 1 left white and right red and switch 2 left white and right red
  • Switch 1 left white and right red and switch 2 left red and right white
  • Switch 1 left red and right white and switch 2 left white and right red
  • Switch 1 left red and right white and switch 2 left red and right white

I tried removing the light fixture so I could check its wall wiring with the voltage tester but I started stripping one of its screws so I stopped.

A few questions:

  • If all six wires are hot (black, white, and red on both switches) is the circuit complete?
  • Should both ends of the light fixture's bulb compartment be hot when the circuit is complete?
  • Could the left side of the light fixture have a blown fuse?
  • When I get the fixture removed if I have a complete circuit will the black, white, and red wires be hot?

Anything else I can try?

New Photos

enter image description here ^ Left white wire is cold enter image description here ^ Left red (!) wire is hot enter image description here ^ Left black wire is cold enter image description here ^ Right red wire is cold enter image description here ^ Right white wire is cold enter image description here ^ Right black wire is hot enter image description here ^ On the left, a working three way switch that powers three basement lights and, on the right, Switch 1 enter image description here ^ Close up of their wires enter image description here ^ Traveler wires for the working three-way switch enter image description here ^ The top left black wire with the white jacket is tied off with the bottom right black wire (next to the stranded ground copper wires) and the switch 2 traveler wires exit through the bottom right of the box enter image description here ^ The ends of the two black wires from the previous photo twisted together with a yellow wire connector enter image description here ^ The fixture's right terminal is hot but the bulb is not working enter image description here ^ Upstairs right switch turned on and the fixture terminal's right wire is hot enter image description here ^ Upstairs right switch turned on and the fixture terminal's left wire is cold enter image description here ^ Tied off white neutral wires in the back of the box are hot with the switch on enter image description here ^ Fixture black wire is hot with the switch on enter image description here ^ Fixture white wire is cold with the switch on

11
  • 1
    Have you tried it with a bulb? On a light fixture, one terminal will be hot and the other is neutral. Both terminals will not be hot. Also, those voltage detectors are meant more to double check for voltage for safety and are not great tools for diagnosing problems - just use a multimeter.
    – JPhi1618
    Commented May 31, 2019 at 14:34
  • 1
    Think of electricity flowing in loops. It comes from the electric panel on a black or red hot wire, but it has to get back to the same panel after it goes through a fixture or appliance. It goes back through the white neutral wires. A hot wire by itself can't do any work unless it can connect back through a neutral.
    – JPhi1618
    Commented May 31, 2019 at 14:51
  • 2
    "same screws" does not distinguish between "selecting screws by position" and "selecting screws by color". Your question discusses positions at length and doesn't say boo about screw color, so I assume the former. Commented May 31, 2019 at 16:24
  • 1
    However that's the configuration that doesn't work. Commented May 31, 2019 at 16:46
  • 1
    you should have power on only one side of the lamp .... if both sides are connected to the hot wire, then the lamp will not light
    – jsotola
    Commented May 31, 2019 at 16:51

2 Answers 2

9

DON'T try random stuff when you get stuck

Trying to replace actual knowledge with "throw things at the wall and see what sticks" is a fatal error when dealing with electrical equipment. Why? The entire strategy is based on stopping when you find "the" combination that works. Actually, many combinations will work and also kill you. The only way to avoid those is skill, so the right thing to do is pause, research and measure.

I'll grant you if you are only connecting to 3-way switches, you can't go too far wrong - but nonetheless, this habit is so dangerous in almost any other context, that I want to address it.

Position of wires on multiway switches is useless

I assume you're changing switches and receptacles for color or style. In that, the most common gotcha (other than broken-off tabs on receptacles) is assuming 3-way switch builders do you any favors by keeping screw positions consistent. "They do not" is the understatement of the year. The only useful indicator is screw color.

Related, electrical wiring is not very well color-coded, and multi-way switch circuits are worse than not color-coded at all. I for one mark wires obsessively, so the next person has a chance of understanding the circuit.

Probably easiest to just "do it the old fashioned way". Travelers are always in the same cable (and are never ground wires obviously). Switch 2 is no help at all. So we look at switch 1. Only two are in the same cable (I can't see, you can) -- gotcha! Those are the travelers. Now, knock wood, that cable is continuous to switch 2, in which the same 2 colors will be the travelers there. (If it stops anywhere intermediate, all bets are off, and this is why I mark wires). Buy a 5-pack of colored tape, and mark all travelers yellow. There is no need to distinguish travelers from each other.

Then, travelers go on the brass screws. The remaining wire goes on black.

Edit: Looking at your photos in switch box 1, it seems clear the travelers are white and red. Wrap them with yellow electrical tape. Most likely they are also white and red at switch 2 (that's not 100% sure but it's the thing to try first.)

The light should have 1 terminal hot

Lights are the ultimate load, and in mains electrical, most loads connect between hot and neutral (unless you dealing with North American 240V or in the Philippines where everything is that). Therefore there should only be "hot" on 1 terminal, not both.


Edit: If the right lamp wire is energized, then most likely the 3-way set is delivering power correctly (it may still be wired wrong for the switches to work as intended).

If power is present at the right, and still it doesn't light, then it's a) burned out bulb. b) burned out socket. Or c) the neutral wire has a problem. There'd be no reason for the latter to happen, given that you don't touch the neutral when replacing 3-way switches.

Your next test is to fit the light bulb and test the left socket. If the left socket suddenly reads "hot", that means there's something wrong with the neutral wire. Otherwise you have a bad lamp or socket.


To answer your questions directly:

  • If all six wires are hot, you need to file a warranty claim on your 3-way switches! The only other possibility here is that your voltage tester is picking up phantom voltage.
  • Both sides of the lamp should never be hot. If it is, and the bulb is in it, that indicates a broken neutral wire. That left side is surely neutral.
  • Neutrals don't have fuses. Their only overload protection is being monogamous to one hot, which is fuse/breaker protected. MWBCs are engineered to allow 2 hots to share 1 neutral. All other sharing creates overloads.
  • Neutrals should never be hot. Travelers are in pairs; one will be hot. Switched-hot will only be hot when the switch is on. Always-hot is I'll give you 3 guesses. Notice I haven't mentioned a color yet. That's because colors don't necessarily correspond to functions. This is why I wrap tape around wires: in my world, switched-hot is red or blue, travelers are yellow in pairs. Here is how your box looks in my world.

enter image description here

(the thin lines are just to make clear which wire is which; the meat of what I do is the band of yellow.) The purple dashed line is a "Chinese Wall" between the left side and right side switches. Because nothing crosses, nothing is allowed to cross. That is relevant if you put a smart switch on the left: it must not steal neutral from the right.

13
  • Precisely! If both terminals were hot, they would be at the same potential and therefore no current would flow. Commented May 31, 2019 at 17:43
  • @Harper thanks for you reply. This is very helpful. I added a few new photos at the end of my post and captioned them. The light was working (the bulb lit up) before I replaced the switches so I know it’s something I did wrong (i.e. I don't think it's an issue behind the wall with the switch 2 travelers). My question is, since the right terminal of the fixture has power when I flip switch 1 on, why isn't the light bulb working?
    – Ryan
    Commented May 31, 2019 at 23:15
  • @Harper I'm supposed to disconnect the switches, turn on the breaker, identify the wires that are not hot, turn off the breaker and mark the wires that are not hot with tape (around their jackets), correct?
    – Ryan
    Commented May 31, 2019 at 23:43
  • @Ryan I completely agree, if the right fixture terminal shows power, I'd expect it to work. The problem is the left side measurement is ambiguous: it may be tied to neutral or may be disconnected. Fit the bulb and test again. If voltage appears at the left side, the neutral is disconnected, which is weird, because changing 3-ways shouldn't have affected the neutral. Commented Jun 1, 2019 at 1:28
  • @Harper - that makes sense. I've tried a few different combinations tonight and can only get voltage on the right side of the fixture, no voltage from the left side. I've tried three brand new light bulbs and none will light up. I even try to refit the bulb, jiggle it around, nothing works. Could the fixture have died during this switch replacement? Anything else I'm missing?
    – Ryan
    Commented Jun 1, 2019 at 2:06
1

Great pics Looks like a bad splice to switch. Or the guy that wired house had his own way of doing it.Most of the time ,black and red are used as travelers White as load out. It seems to be a dead end 3 way splice. The one box with the problem may be, the one with the 3 wires.White to black screw, red black on brass as travelers.White wire should be made a black color .It is not a grounded conductor.(not neutral).If you did not touch any other switches.Put white on black screw black red on brass, If you did work on other 3 way Should work.and are they the upper switches. That does not work send pic of the other switches .

11
  • Thanks Robert. Should the hot wire should go in the black screw on the switch?
    – Ryan
    Commented Jun 1, 2019 at 0:48
  • I just posted new photos of both sets of three-way switches under the light fixture at the top of the stairs. The left switch's set of wires has a hot red wire and the right switch's set of wires has a hot black wire. Connecting each hot wire to the black screw on their respective switches, and their travelers on the brass screws, does power the fixture's right terminal but it still does not power the light bulb.
    – Ryan
    Commented Jun 1, 2019 at 1:23
  • If you think you are getting power from the hot wires, and they turn off and on.Up and down ,,Not the switch ,,..Bad light socket or ,,Pulling wires out loose wire nut in white wires .I think It is light .Should read 120 if you take light off. Bad socket happens a lot with that light .
    – user101687
    Commented Jun 1, 2019 at 1:43
  • Thanks Robert. I think it has to be the light fixture at this point. I've tried everything else I can think of.
    – Ryan
    Commented Jun 1, 2019 at 2:10
  • Take off light check power.