I'll be adding a new 60amp GFCI breaker to the panel.
OK, first let's hit the regenerative brakes on that charge speed. That is a BONKERS charge speed for home charging. First, I advise reviewing Technology Connections' very common-sense video about home charging, and if you want the part about sizing level 2 circuits, that's at 28:15.
https://www.youtube.com/watch?v=Iyp_X3mwE1w&t=1695s
Now, if you want to slap a new 60A load onto your panel, unless you cheat (more on that later) you need to have the service capacity needed for the job. That is determined by your AHJ, but most want you on NEC 220.82, this worksheet here. Note line 2 applies only to your 2-3 kitchen general-use receptacle circuits, not other rooms and not circuits dedicated to dishwasher, disposal, microwave etc.
Now, if you've tempered your requirements per Alec's video, and you still don't have room for your EV capacity per your Load Calculation, then back goes that Chargepoint and get one of the few stations capable of EVEMS, which auto-adjusts EV charge rate on the fly to protect the panel from overload. Some vendors' EVEMS can also do solar capture, or direct to the car exactly the solar power you'd otherwise be exporting to the utility.
The other thing about wiring is that lots of people (to save a measly $30) want to run wires at their absolute thermal limit. EV charging is the most brutal load a house will ever see. Especially if someone operates in gas station mode and doesn't recharge til near empty, resulting in a many-hours-long session where thermal rise can really overcome thermal mass. So running a wire right up at thermal limits is not something I recommend. Such hot running wires tends to uncover every flaw in an installation and make it crispy. Now were you planning to use a torque screwdriver per 110.14? Case in point on those "flaws".
The GFCI is required because the new circuit is in the garage (210.8.A).
It does not say "breaker". The GFCI protection can be provided by a GFCI receptacle. And happily, if you look into what an EVSE ("charger" but not) actually is, It Is A GFCI Receptacle... really.
"How can it possibly be a receptacle? It has a cord on it!" Not necessarily. The new J3400 standard specifically authorizes untethered stations, with a J3068 socket on the wall instead of a cord. You cannot possibly deny a box with a socket is a receptacle. OK, so adding a cord changes nothing to the equation. It's still a receptacle.
The nominal load of the charger is 50amps so 60 amp is appropriate.
No it isn't. 50A EV charge rate requires a bunch of things. First the circuit must be 62.5A because of the 125% rule in 625.42. Second, because the circuit is now over 60A, a disconnect switch at the station is now required per 625.43.
Clearly, a "ChargePointy-Haired Boss" told the engineers (in Cave Johnson style) "I want a 50A station! 2 amps more than the other guys." The engineers facepalmed and said "But no car on the market can usefully use that. They all stop at 48 amps, except for a few larger vehicles which go all the way to 80 amps (and for them, stopping at 50A is silly, and you might as well go to 80A). Also, that will kick in the disconnect rule per 625.43." Anyway, cPHB won that argument, so we have this weird wart of a product obliging us to explain all this stuff to people.
I'm ignoring the part where GFCI breakers over 60A are unobtanium, because you don't need a GFCI for a hardwired unit.
(I wanted to use schedule 80 PVC but the big box stores are out of stock).
IME big-box stores don't sell sched 80. I'm a bigger fan of EMT anyway since it's not glued, so easier to correct defects.
The charger I'm installing can draw as much as 50 amps and calls for a conductor compatible with 90C.
They are saying their terminals are rated 90C. This is relevant to 110.14(B) but is not relevant to anything in a dwelling, as panels are not rated 90C, and limit you to the 75 number in any case. The 90C columns in table 310.16 may as well not exist.
Ill be using THHN AWG 6 copper which is rated to 65 amps and 90C (B.2(1)). Total wire distance is less than 35ft.
WHAT??????? You just said you were only using conduit as a damage shield to run up the wall. You didn't say anything about running conduit the entire way box to box. You can't run THHN wire not in a conduit.
If you don't want to run in a conduit, you have to use cable. If you need 75C rated cable, look at SER or MC (or SEU if you can find it).
Question 1: My charger only uses the two hot lines plus a neutral. What gauge does the neutral need to be? Citing the code for an answer would be appreciated.
Wow, novice. All your code cites don't reflect any real knowledge, eh? Yeah, these huge "swiss cheese" knowledge gaps really show what happens when someone tries to plink knowledge off a search engine or AI. The thing only answers questions, it doesn't tell you which questions to ask. NEC itself says that in 90.1: "Not intended as an instruction manual for untrained persons". Please get a book or courseware which is intended for that. Everyone needs a well-rounded primer on the subject, so they know which questions to ask.
Anyway to your question, a) No EV uses neutral, see J1772 and Tesla port spec. And b) No EVSE needs neutral, see NEC 110.3(B).
I will be direct wiring the charger. The hole for direct wiring is on the bottom of the charger while the wires will be coming from above. Is there an elegant way for the wires to do a 180deg turn?
NEC 110.3(B) read the installation instructions. Many stations accept top entry, I would just get one that does. The Chargepoint is kind of a dopey unit, as you can tell from the lack of EVEMS, the 50A limit and the fact they had to introduce a whole new model (the Flex) just to provide adjustable amp rate. And many of us are very suspicious of their aspirations to product-ize and monetize their users. ChargePoint wants "charging as a service". If you have some weird thing where you want that, ask for better options.
I've read that water can condense on the inside of the EMT conduit. This can be addressed by adding weeping holes along the conduit. Should I be worried about this / address this?
That's only a problem if it goes outdoors.