At home I installed a CHFN120A1CS on a circuit with a single overhead LED shop lamp with a 0-10volt type dimmer switch controlling it (Leviton ip710), nothing else. Single run of 12-2 from the panel to the dimmer, then dimmer to the light, about 25 feet total length.
Upon energizing the CHFN the first time, with the overhead shop LED lamp off, I saw the breaker’s “power up” 1-2-3 light flash in the first half second, it was just a single flash. Status key says that means “electronic overload protection is turned OFF: This is uncommon.” No information on what to do to investigate/resolve the issue, or why the ‘uncommon’ issue is important enough to have a status indicator and zero other information.
Next, I tried verifying the breaker’s electronics are operational by pressing TEST. The breaker tripped, when turned back ON, again fast single flash at startup, but then after about 5 seconds the breaker red LED stays solidly lit, no blinking pattern. This has survived several rounds of testing; all wires are verified in the correct spots on the dimmer switch.
For the quick single flash at start up, there is an unanswered post here: Eaton AFCI/GFCI breaker is only blinking once when turning it on
And for the red LED staying lit, I’ve found a post that purports to be Eaton saying that, is okay and just due to tight tolerances in the design confusing the circuit and always showing the LED (which is, um, an interesting answer)
https://www.reddit.com/r/electricians/comments/k7zpo1/eaton_breaker_solid_red_light/
Is the red LED light staying solid a problem? And what can be done about the first issue, the single flash at startup indicating that the “electronic overload protection is turned OFF”?
The overhead LED lamp and dimmer seem to be working perfectly fine when the breaker is ON, just the red LED status light on the breaker doesn’t make sense.
Is this breaker functioning properly, anything I can troubleshoot?
Thanks
Aaron
First update, 2 Jun 2021: This is the exact response from Eaton when I sent them this question:
The breaker is functioning just fine. The light behavior in normal condition varies from breaker to breaker, as long as it does not trip and flash a code, there is nothing to worry about. You may even see flashes sometimes when the breaker is in normal operation, and again, that’s normal. The flash codes are to be referred ONLY if the breaker trips, else you are good to go.
I sent a follow up question. I just can't easily accept that the only condition that indicates failure (1 blink at startup) is being indicated, but that it should just be ignored because, hey, we can't make a consistent product, my paraphrase.