2

Recently purchased land that had a meter pole with a mobile home server feed on the meter pole. I built a 10x10 shop and added a 200a Square D HOM3060M200PCVP. It's WAY oversized for what I need. I recently had a 16'x28' "shell house" build (outside complete, inside is studs). I had the regional service provider out (Oncor) and he told me to feed the new house with 2/0 triplex through the shop box. As far as I know, I can't add feed through or pass through lugs to the existing box.

I can replace the shop box with a smaller (fewer breakers) one and put the old one in the house, But what I want is a split box to take the 4/0 service feed and split one to the shop, the other to the house. I would like to mount the split box on the outside of the shop, but inside is okay. Main issue is the 4/0 service has been cut to the shop box. There is not much room, but I can put it inside between the floor and the new box.

My issue is, I can't find a triplex split box for 4/0 wire. Service to shop was about 60'. Shop to house will be about 50'. Shop box was mounted upside down for the feed coming in from the floor. If the existing Square-D will let me add a pass though, I have room to loop the cable back out the floor and to the house.

Anyone know how I can get service to the house without spending a a ton of money?

12
  • Are you OK with the shop box disconnect turning power off to the house? That's going to be the main governing factor in what you do here (although it's possible to do it both ways, it requires different parts for each configuration). Also, can you post a photo of the inside lower part of the shop panel with the power off at the pole and the cover removed? Commented Apr 20, 2020 at 23:55
  • 1
    +1 for getting a "way oversized" panel. We like contributors but we're also happy when their question isn't "how to cope with a full panel?" :) Seriously though, on your house panel, do yourself a favor and get a 40-space and leave the 30 at the shop. 30 is tight for a full house, especially when you have 200A service and heavy electric appliances are an option. And double especially under NEC 2020 where everything has to be full size breakers (no more double-stuffs). Commented Apr 21, 2020 at 1:11
  • Also, how many wires are in the existing 4/0 run from the pole to the shop panel? Commented Apr 21, 2020 at 1:52
  • I should have added that the "house is only 450 sq. I will have full size washer/dryer, gas water heater and toying with gas vs ele range. I don't see the draw on the house being that much nor needing a lot of openings in the panel. Size is more the issue but a 40 vs a 30 is nothing. Commented Apr 21, 2020 at 13:06
  • I purchased 4/0 4/0 4/9 2/0 wire for the service feed, but once I put the wire in, I just grounded the shop using a 8' grounding rod. I'll do the same to the house, but I'll use 2 this time. Also, in the county, so I can do what I want. If a pro did it, he would have to get county permits. I wish I could afford a pro, but in these times, yo do what you can. Commented Apr 21, 2020 at 13:12

2 Answers 2

0

Your first problem: you have your services and your feeders mixed up

The bad news for your situation is that the first order of business here is cleaning up your installation. You see, that mobile home panel is your service disconnecting means, and as a result, nothing that comes out of that box can be treated as a service; it's either a branch circuit (to outlets) or a feeder (to more panels). In turn, this means that you need to separate neutral and ground everywhere downstream of that box, including at other structures. Fortunately, your utility bailed you out and provided you with cable that had the right number of wires in it (quadplex, not triplex), even though you missed the hint they were giving you there. As a result of that fortuitious turn of events, all you need to fix this is

  • A PK23GTA ground kit with a LK100AN add-a-lug
  • And a 2/0 add-a-lug for your mobile-home box.

First, mount the add-a-lug to the neutral/ground bar in your mobile-home box (service equipment) as per its instructions and connect the capped-off 2/0 to that add-a-lug, thus making that 2/0 into a grounding wire. Then, you can fit the PK23GTA to the shop panel followed by fitting the LK100AN to the PK23GTA; once again, follow the provided instructions. From there, you can connect the 2/0 in the shop panel to the LK100AN. This then lets you move the existing branch-circuit grounding wires to the ground bar; if you need to extend a few using wirenuts and 10AWG green or bare wire, that's fine. Once that's done, you can then move the grounding electrode conductor from the lug it's on over to the ground bar (where it belongs), then finally remove the green bonding screw from the shop panel's interior so that neutral and ground are isolated at your shop panel as they should be.

Sidebar: What if you can't find an add-a-lug for your mobile home box?

In the off-chance that you can't find an add-a-lug for your mobile home box, perhaps because the box is of a type no longer made, there is still a way to hook the grounding wire up to the box. Instead of the 2/0 add-a-lug from above, you'll need for this:

  • Some sandpaper to remove paint from the inside of the mobile home box
  • Two 10-32x1/2" self-drilling ground screws (Garvin part number GSST)
  • And a T-style, 14-2/0, UL listed mechanical lug (IHI part number T2/0, available from lugsdirect.com)

First, with the box powered off, you'll need to pick a spot on the inside back of the mobile home box to mount the lug, so that there's at least 3" of room from that lug to any obstruction in the direction you want the wire to enter the lug (stood up vertically along one side of the back should work), and sand the paint off about a 5/8" wide by 1-5/8" tall section of the inside back surface, below live parts, so that good metal-on-metal contact can be made. Then, you'll want to line the lug up with that bared spot, and screw it in place using the Garvin GSSTs through the provided mounting holes in the lug. Finally, you can attach the 2/0 grounding wire to your new lug, just as if it were a factory add-a-lug.

However, this isn't as hard as you are making it sound

The good news in your situation is that what you want (the feeder basically making a T-junction at the shop, with one leg going into the shop panel's main breaker and the other leg continuing on to the house) is possible for not too much money (under $200, once you've taken care of sorting the grounding situation out), provided "some assembly required" does not scare you off, and you're OK with a slight Code fudge (225.31/225.32, with the idea that the tapped feeder conductors can continue on without a disconnecting means at this building) due to the location of the existing shop panel (namely, indoors). You'll need for this:

  • 3 Eriflex SB2C250 (aka 561170) UL 1953 listed power distribution blocks (these go for $50 apiece online, Galco and Allied both carry them)
  • 6 #10-32x1/2" sheet metal (i.e. self-tapping/self-drilling) screws (for mounting the power distribution blocks) -- Garvin GSSTs will do in a pinch
  • About 6-8' of 4/0 Al XHHW-2 for making jumpers in the panel
  • Another LK100AN for the shop panel's ground bar
  • And an inch-pound torque wrench for making up the connections

Once you have the power off at the pole and the deadfront removed from the shop panel, you can start mounting the power distribution blocks; these go into the gutters on either side of the panel, near the bottom, with their two-hole ends facing downward. One block goes on the same side as the ground bar, mounted to the back of the loadcenter cabinet (the "box" part of a "breaker box") using two screws into the back, as far to that side as possible, and about 6" up from what is currently the bottom of the box. Across from that block, on the other side of the box, go the other two power distribution blocks, dovetailed together and mounted using two screws apiece, horizontally aligned with the first block, but as far to the other side as possible.

Once they're all fastened down, you'll need to pop the covers off them and start hooking the wires up. The hots and neutral get removed from the existing lugs and moved over to the bottom of their corresponding power distribution blocks, one hot on each side, with the neutral going to the remaining block. From there, you jumper back to the existing breaker/neutral lugs with some of that 4/0 Al XHHW-2 single-conductor, going from those lugs to the other lug (hole) on the bottom of said blocks. As you go, you'll need to torque these connections to their specified/labeled torques (275 in-lbs for the block lugs, 250 in-lbs for the main breaker and neutral lugs); this is a NEC requirement nowadays, and also good practice, lest your electrical system lose you the race! Once everything's made up connection-wise, you can pop the covers back on the distribution blocks and attach that second LK100AN to the opposite end of the ground bar from the existing add-a-lug using the provided instructions, so the outgoing ground has a place to land.

With all that done, you can button your panel up, turn the power back on, and label the shop panel's directory with the fact that the feed-through conductors needing to be disconnected back at the pole, as is required by NEC 312.8(A). When you put the house feeder in, you'll need to use one of the large knockouts at the current top rear of the breaker box to exit to a nipple and LB for the drop down into the ground, with the quadplex hots and neutral landing on their corresponding distribution blocks, and the bare ground in the house quadplex landing on the spare LK100AN provisioned for it.

4
  • DUDE - you are a life saver!! Even the guys at the electrical supply could not tell me this (although, I think they just had the warehouse guy filling order, not an electrician). This is EXACTLY what I needed. Thank you so much!!! Commented Apr 27, 2020 at 14:04
  • @ChrisWeaver -- a couple of little questions so that I can help you with the fine details: first, what make/model is the existing mobile home box? second, does the feeder going into the shop panel come in via the bottom of the panel, or via the back of the panel? Commented Apr 27, 2020 at 23:11
  • No idea, I think it was put there around 1985, hard to tell using google maps history. The shop feed is coming in through the floor (direct burial) and the box is flipped (200a on the bottom). The bottom of the panel is about 3.5 feet off the floor. I can move that panel into the house and buy a different panel for the shop if it makes things easier. Commented Apr 29, 2020 at 14:03
  • @ChrisWeaver -- keeping the existing panel at the shop is fine I reckon. You'll need to know what make the mobile home box is in order to get the correct add-a-lug for it, BTW Commented Apr 29, 2020 at 23:19
1

If allowed in your jurisdiction, I'd go with a class 320 service. You could power the shop and the house off the same meter base. Both panels would be considered the "main panel" so no need for a 4 wire service. I just did this with my sons house that I'm doing most of the wiring on. I also have a class 320 (320 amps) to my 2 200 amp panels in my house. It's a practical solution, depending upon the exact layout.

Here is a link to the meter base I bought for my sons house: https://www.amazon.com/gp/product/B008KM7LZM/ref=ppx_yo_dt_b_asin_title_o01_s00?ie=UTF8&psc=1

3
  • Yeah, I wish OP hadn't installed triplex. But if your idea is legal in OP's jurisdiction it's an ideal situation. Commented Apr 21, 2020 at 1:13
  • Thanks, Harp. I just don't know why ppl go for small panels. The cost difference is so small compared to breakers, possible rework later, etc. I think sometimes ppl think it's not code legal to have a large panel fed by feeders less than the panel rating. You and I both know that's not the case, it's just a matter of the gauge of the feeds and the right overcurrent protection. sigh Commented Apr 21, 2020 at 2:53
  • OP here - The land came with a mobile home feed through panel and I did not want to pay the ele co to pull the meter so I could re-wire the whole thing like it should be. Eventually, I will have multiple houses so It will have to fix this mess. I had the service provider for my area (Oncore - East Texas) come out to get a new service to the new house and he is the one that suggested I just feed off the shop. I update my original post with more info but no, I don't really want to pass through the shop, I want to split before the shop and power both from the service separately. Commented Apr 21, 2020 at 13:32

Your Answer