6

We live in a building with 220V service with primarily 110V outlets but a few specialty ones at 220V.

Earlier this week electrical service in half the building across all three apartments went out. The utility company came out on an emergency basis and restored power by bridging one of the 110V wires onto the faulty one.

Now the lights are back on but the 220V outlets are presumably only offering 110V. It is safe to run a 220V electric dryer on an outlet that now offers 110V of power?

I called the manufacturer of the dryer (Samsung) and all they knew how to do was look up stuff in the manual, which was not helpful. The emergency service technician (not a electrician) was not certain either. I called an electrician and he didn't seem certain either, but recommended against it to be on the safe side.

From the research I have done it seems like the concern might be that the motor might burn out possibly and that definitely the heating element would not get as hot so it might take a lot longer for a load to dry. I can live with the latter but not the former. Additionally are there any safety issues to consider?

I tried the dryer for a moment and the panel lit up and the drum spun as expected. Did not test to see if it got hot.

Repair service is a scheduled for a week away and the laundry is piling up! Even when they attempt repair they are counting on running a new wire through the underground conduit which I already suspect is not sound so they may have to dig which will surely take longer.

2
  • 6
    If you call Samsung support, (1) you're not going to get someone with an EE degree, and (2) even if you do that person isn't going to whip out the schematics and prove and disprove that it's safe; they will refer you to the manual which specifies the operating voltage for the unit in the same way as a regular customer support rep.
    – Kaz
    Commented Sep 20, 2019 at 18:17
  • 3
    That said, appliances have to be capable of handling under-voltage without causing a safety issue. This can happen in brown-outs.
    – Kaz
    Commented Sep 20, 2019 at 18:20

2 Answers 2

20

It won't work. Your 220V (really probably 240) outlets will actually have 0V, not 110V.

The reason for this is that normally the 220V outlets make their 220 by taking both 110 lines that are out of phase with each other, such that while 1 is at +110, the other is at -110 for a difference of 220. Since the power company bridged one of the 110 lines to make up for the dead one, that won't work -- they'll both be at +110 or -110 at the same time, for a difference of 0.

9
  • 2
    I tried the dryer for a moment and the panel lit up and the drum spun as expected. Did not test to see if it got hot. Have updated question to reflect this fact.
    – AllInOne
    Commented Sep 20, 2019 at 17:43
  • 7
    @AllInOne, yes, that's not unexpected. Many dryers use 120V for the motor and controls, and 240V for the heating elements. All the 120V parts of the dryer will still work, but the 240V parts will not work at all, so I would expect that it won't produce any heat.
    – Nate S.
    Commented Sep 20, 2019 at 17:44
  • 2
    The panel and spinning is done via 120V. I think the heater is the only 240V equipment in there. Look around for a local laundromat. Commented Sep 20, 2019 at 17:44
  • 2
    You're good for "air fluff"
    – JACK
    Commented Sep 20, 2019 at 17:58
  • 3
    One could plug a hand held hair dryer in nearby and aim it at the intake vent of the dryer in "fluff mode". It would still take forever, but slightly less time than without it (assuming a breaker doesn't trip)... ;-) Use a laudramat until it is all fixed... your dryer will not work.
    – JRaef
    Commented Sep 21, 2019 at 1:39
7

Most North American style dryers will work on 120V power one of two ways:

Make both hots (the same pole of) 120V, neutral is neutral

In this case, the 120V equipment on the dryer will work. It is not guaranteed to be this way, but likely it will be the timer, controls, blower, and tumble motor. So it can "air fluff".

However, the heat will not work at all. So all you get is air fluff.

This is the setup you are getting by default, due to the way the power company has emergency-bridged it.

Move one hot to neutral

And this modification should be done inside the dryer not by altering the plug or socket. The dryer should be rendered safe in any case, so that nothing spits and sparks if power changes. E.G. Don't lug both of the cord's hot wires together.

In this case, you pick the right hot wire (on the dryer's side) and move it to neutral. If the tumble motor/fan/controls stop working, you picked the wrong hot. Undo it, then use the other hot.

At this point, the tumble motor and fan will work, as will the controls (on most dryers).

Heat is a bit of a problem. It will work, but only at 1/4 power. This is better than nothing but expect drying to take awhile.

By the way, this will require less than 20 amps of power. You could make a dryer work this way on a 120V/20A circuit, because it would draw less than 16A (80%). You would have to measure to see if it uses less than 12A (80%) before putting a common 15A plug on it.

6
  • 3
    I'm not sure I'd advise OP to move the hot to try to get some heat working in this situation. Since the entire building is now drawing all its power from one leg, if too many people start to do this, it may well blow the utility's fuse on the remaining phase, and then they'd have no power at all. They may get lucky, but personally I wouldn't risk that given that it won't be very effective at drying clothes anyway.
    – Nate S.
    Commented Sep 20, 2019 at 21:13
  • @NateStrickland - Then they'd have to actually run a real temporary line (shrug). +1 at Harper and you. Can it be done: yes. Should it: no.
    – Mazura
    Commented Sep 21, 2019 at 2:29
  • @NateStrickland -- if the load of a dryer at 1/4 heating power is enough to take out the remaining leg, then something much deeper is awry... Commented Sep 21, 2019 at 2:43
  • @ThreePhaseEel, Nate didnt say "a dryer", he specifically said, "if too many people start to do this". Commented Sep 21, 2019 at 18:39
  • 2
    1/2 the power is available and the reconfigured dryer draws 1/4 the power. For what it's worth. Commented Sep 21, 2019 at 18:49

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.