I would like to use my garage lighting circuit for my garage door opener but I need to extend it 5 feet.
The lighting circuit is 14/2 wire but I have 12/2 wire.
Should I buy a 6 foot piece of 14/2 wire or could I use the 12/2 wire for that length?
I would like to use my garage lighting circuit for my garage door opener but I need to extend it 5 feet.
The lighting circuit is 14/2 wire but I have 12/2 wire.
Should I buy a 6 foot piece of 14/2 wire or could I use the 12/2 wire for that length?
Keep in mind if you use the lighting wiring to power the opener, whenever the lights are off the opener will not work.
Just use the 12/2. You're always allowed to upsize wire.
How does that work with circuit rating? The smallest wire on the circuit decides the circuit rating (in amps) so the smallest will still be 14 AWG and the circuit will still be 15A.
Now, you have to watch your connections. Wire-nutting 12 to 14 is no problem (I nut 12 to 18 all the time). If your receptacle uses back-stab connections, those are not compatible with 12AWG wire, so you'll need to use the screws. However you can't mix screws and stabs, so you'll need to use the screws for all the wires. The $3 screw-and-clamp type receptacles help with this (they can also handle 4 wires per side!)