Sep 9, 2019 at 12:43 | vote | accept | Superhuman | ||
Aug 10, 2019 at 22:05 | comment | added | Retired Master Electrician | What is the calculated power demand you are trying to use the inverter for? Most inverters and ups' only have a 15 or 30 minute supply at 80% of the output. How long are your outages? | |
Aug 10, 2019 at 18:23 | answer | added | Ecnerwal | timeline score: 1 | |
Aug 10, 2019 at 18:20 | comment | added | JACK | Zero downtime??? Most of the switching is break before make. | |
Aug 10, 2019 at 15:37 | comment | added | ThreePhaseEel | Where are you on this planet? What make and model is your existing inverter? Why do you need a 0-downtime switching setup? (Most devices any more can deal with a 16-20ms switching delay without any loss of function.) | |
Aug 10, 2019 at 14:43 | comment | added | Solar Mike | There are inverters that will use the primary input and switch in or out other sources as necessary seamlessly. Trace spring to mind. | |
Aug 10, 2019 at 14:40 | review | First posts | |||
Aug 10, 2019 at 15:06 | |||||
Aug 10, 2019 at 14:37 | history | asked | Superhuman | CC BY-SA 4.0 |