The boiler is used in a central heating system to heat water that is pumped through pipes to radiators within the home.
1
vote
Accepted
How to make c-wire to a new boiler using Fast-Stat common maker?
This is fairly simple
According to the ladder diagram for your system, the thermostat simply connects transformer R to the call-for-heat signal on your control board, so this is straightforward. You …
1
vote
Accepted
How to connect C-Wire to Weil-McLain Boiler CGa Series 3
The red wire then lands on Rh, with the white on W, as you'd expect; this means that your boiler won't confuse your thermostat if it ever malfunctions and cuts out on low water, overtemperature, or such …
1
vote
Neutral Wire on Oil Boiler
Wiring-wise: you have the correct idea
Your proposed wiring scheme (R to R/Rc, G to W1, and C to C) is correct for the boiler you're working with; this can be deduced from the wiring diagram supplied on … require turning off automatic home/away detection to prevent it from causing daily recovery swings, as well as configuring the thermostat as described above to avoid uncomfortable "short cycling" of the boiler …
0
votes
Accepted
Where can I install a C-Wire for Weil-McLain gas boiler? (EGH 115, 4 Series, Natural gas)
I'd strongly recommend getting a steam-boiler veteran out there to rearrange the controls on your boiler so that you can provide constant 24VAC to your thermostat. … This way, the Nest gets a constant 24VAC supply, yet breaks the thermostat circuit on the boiler in the place the boiler expects it to, to avoid interactions with the low-water cutoff and that aquastat …
1
vote
Accepted
Rewiring a boiler’s c wire for a smart thermostat
As it turns out, C is staring you in the face
As it turns out, the transformer is sitting right in the middle of your photos, and by matching the wiring diagrams from your boiler's installation manual …
0
votes
Accepted
Connecting a C-wire to a Burnham Independence Boiler
Connect C to the wire-nutted bundle of yellow wires
According to the manual for your unit, the C-wire coming off your transformer is a yellow wire (we know this because the manual has it connected to …
3
votes
How to track energy usage per zone?
Since tenants are involved, you'll need to do this right
If you were owner-occupying a zoned single-family dwelling, then taking shortcuts in the interest of expediency would be an acceptable way to …
2
votes
Can't get wifi thermostat to work with gas boiler
You'll need a relay here
Your boiler, in addition to using nonstandard wire nomenclature, does not provide 24VAC power directly to the thermostat. … One relay contact terminal (the COM terminal) jumpered to the Y terminal on your boiler
The other relay contact terminal (the NO terminal) jumpered to the G terminal on your boiler
And the red wire from …
1
vote
Accepted
How to connect c-wire to Burnham Series 2 boiler?
Tap the white wire in the control harness
If you look closely at the wiring diagram for your boiler -- there is a 9 pin connector with a harness connected to it that connects to the thermostat wiring … Install your Ecobee, turn the boiler back on, and enjoy! …
1
vote
Accepted
Zone Controller T-Stat Wiring w/ 24V transformer, isolation relays for 2 zones
The relay contacts then simply go in parallel -- this means that a call for heat from either thermostat will fire the boiler. …
1
vote
Accepted
Is there harm in using my mini-splits in conjunction with my hot-water baseboard heat?
Running them at the same time won't cause breakage
As Ed Beal indicates in his comments, running both systems simultaneously with the mini-split set for heating won't cause trouble -- in fact, your m …
1
vote
How to handle unattached ground wires in boiler fusebox/control panel (sub-panel?)?
Add a ground screw and land the ground wires there
I'd use a self-tapping ground screw (Garvin GSST or equivalent -- these are different from regular sheet-metal screws in that they use a fine-pitch …
1
vote
Accepted
Condenser is always running
You have a short in your wiring
Somewhere in the wiring for your HVAC system, Rc has shorted to Y. Find the short and fix it (using electrical tape to insulate the shorted wires will work for now gi …
0
votes
Accepted
Nest thermostat not turning on heat
Try switching the wire connecting the Nest's W output to the Nest's G output and seeing if turning the fan on causes the boiler to fire up. …
1
vote
Is the control wiring for my boiler reversed?
Putting the switching in the C wire, as the installers of your setup did, works, but has the undesirable side effect that grounding out the wiring from the zone valve to the thermostat or boiler control …