I have a 30amp pool subpanel wired with 10awg THHN through 3/4" schedule 40 PVC conduit. I'm considering installing a heat pump pool heater which will require a beefier subpanel.
Can I run 2x 4awg hot/hot and 1x 8awg neutral through the conduit and utilize a ground from a nearby junction box to serve as the subpanel ground? This is about 38% fill which would be a beast to pull particularly through old conduit, but seems like it would fit.
Most of the pool loads are 240v, so undersizing the neutral to the grounding conductor size seems appropriate based on calculated load. The only 120v load is the pool light and a receptacle for a powered pool vacuum. This would allow me to have an 80amp breaker to protect the sub panel.
Pool pump is ~10.1 amp 240v load, pool heater is 37amp 240v load. In the future I would like to add a second pump and possibly a second smaller heater so I'm trying to maximize available capacity.