I bought a UL-listed electric fireplace a couple years ago and I'm still trying to confirm everything is normal and safe in the winter. This is a 1500 W (12.5 A) cord and plug appliance running on a 15 A circuit in the USA.
I've already replaced all the switches and receptacles to remedy grounding and backstab issues. Also replaced the breaker with an AFCI type.
I still get slightly different results with this appliance depending which receptacle I use. So today I decided to test the circuit voltage to see what's really happening.
I want the fireplace to run off receptacle R6 for placement, and I'm taking measurements at R8. With appliance turned off, I'm getting almost exactly 120 V hot to neutral and 0 V neutral to ground.
With the appliance on, I'm losing 7 V. The meter shows 113 V hot to neutral, 116 V hot to ground, and 3 V neutral to ground.
When I run the appliance off receptacle R3, it improves to 117 V hot to ground and 2.3 V neutral to ground.
To make it a fair test, I also tried running the appliance off receptacle R9, and the numbers dropped to 114 V hot to ground and 4.5 V neutral to ground.
Is it typical to get that much extra resistance and voltage drop just from using different outlets in the same room?