I am replacing all of the electrical in my house and am upgrading from a 200amp service to a 320amp service. We are in an unicorporated area of the county so there will not be an inspection but I still want to do things safely. Before I purchase thousands of dollars worth of equipment and wire I want to make sure that my plans are good. Any advice is much appriciated! Here is what I am planning.
There will be 2 200amp breaker panels in the house (one about 30ft from the meter base and another about 80ft). To safely power each panel, I would connect the two hots and neutral from the meterbase and run those a few feet through conduit to a 200amp disconect use 4/0 AL wire. Since each of the disconnect boxes are the first point of disconnect I would have the netrual and ground bonded in each of the boxes. From each of the disconnect boxes I plan to run 4/0-4/0-4/0-2/0 AL SER cable thorugh the attic (not in conduit) to each of my breaker panels. In the panels the netrual and ground would be disconnected.
One question I have is can I use the same two grounding rods to ground both of the disconnect panels or do I need two rods for each panel?