I am installing a receptacle in a confined space inside some custom cabinetry, so I need to use the smallest (with respect to depth) box I can that still meets code. This is a remodel so the wire itself is already in place. The box will have two 12/2 romex, one line, one load, plus 3 pigtails to the device (ground, common & hot). Pretty much the standard setup that I've seen in most receptacle boxes.

I've been trying to puzzle out the minimum box volume that I can use by reading the NEC, etc. But I don't see any indications of if I need to take the pigtails into consideration.

My preference is to use a pvc old work box because the install is into a cutout in 3/4" hardwood panel. There are no studs or such that suite for a typical new work box install. The largest 1-gang old-work box that I seem to be able to find locally is 23 cu.in. It fits my space but seems small for that much wire.

I did find this question: Box Fill Calculations Help Please - Two Romex 12-2-2

If I follow the math therein, I have 4 wires + 1 ground + 2 wire/equiv for the device = 7 wires x 2.25 cu. in. per wire for 12ga = 15.75 cu. in. That seems really tight. So is this right?

4
  • Don't count the pigtails. Last sentence of 314.16(B)(1) "A conductor, no part of which leaves the box, shall not be counted." Commented Jul 2, 2023 at 15:31
  • Steel old work boxes exist, and are better than PVC on several points. So defaulting to a PVC box is not particularly an obvious choice to anyone with experience.
    – Ecnerwal
    Commented Jul 2, 2023 at 15:33
  • To answer this question I would simply have to rote repeat this answer. diy.stackexchange.com/a/260108/47125 (with 8 conductors changed to 4). Commented Jul 2, 2023 at 17:01
  • Why are you pigtailing at all? Only thing you'll need to pigtail is the ground. The hot and neutrals both get connected to the outlet.
    – Huesmann
    Commented Jul 3, 2023 at 12:42

1 Answer 1

4

Any box at minimum size for wire fill IS really tight. Normally we choose to avoid it, but if you need to go there for practical reasons other than easy installation, you appear to have the math correct, assuming your PVC box is the typical sort with no internal clamps to account for.

Pigtails that don't leave the box are explicitly not counted in wire fill calculations. Only wires that pass through or terminate in the box count.

Mind, you don't actually have a need for pigtails, so you can simply connect the incoming wire to one set of terminals on the receptacle and the outgoing wire to the other set of terminals on the receptacle. But that does not change the required space for box fill at all.

Please stop referring to neutral as common. It's not.

For the smallest "with respect to depth" boxes, look away from single-gang as a box format; instead, look to a 4x4x1.5 with an appropriate cover plate to mount your device yoke to.

1
  • Thanks for confirming. A 23 cu. in box fits my space so I won't be scraping the absolute minimum thankfully. And thank you for catching my misuse of 'common.' I'll blame my old brain and the fact that I don't deal with this nomenclature all the time. These days, my head just grabs the wrong word sometimes and I fail to catch it. Glad you did. As for the 4x4 box, yes that would work well from a practical point of view but doesn't meet aesthetic requirements for a kitchen island. Commented Jul 3, 2023 at 11:38