I am installing a receptacle in a confined space inside some custom cabinetry, so I need to use the smallest (with respect to depth) box I can that still meets code. This is a remodel so the wire itself is already in place. The box will have two 12/2 romex, one line, one load, plus 3 pigtails to the device (ground, common & hot). Pretty much the standard setup that I've seen in most receptacle boxes.
I've been trying to puzzle out the minimum box volume that I can use by reading the NEC, etc. But I don't see any indications of if I need to take the pigtails into consideration.
My preference is to use a pvc old work box because the install is into a cutout in 3/4" hardwood panel. There are no studs or such that suite for a typical new work box install. The largest 1-gang old-work box that I seem to be able to find locally is 23 cu.in. It fits my space but seems small for that much wire.
I did find this question: Box Fill Calculations Help Please - Two Romex 12-2-2
If I follow the math therein, I have 4 wires + 1 ground + 2 wire/equiv for the device = 7 wires x 2.25 cu. in. per wire for 12ga = 15.75 cu. in. That seems really tight. So is this right?