I'm running a circuit through a basement rim joist to a PVC LB connector on the exterior of the house via a short pvc stub glued to the LB connection but just free on the basement rim joist side.

Can I just run romex directly through the unachored side of the stub and connect to the THWN in the LB or must I use an electrical box to protect the basement side?

If inside a box there would still be no way to anchor the stub directly to the box with a connector because then the box would not sit flush to the joist but the box and the LB are anchored and everything is protected. Is there another way?

enter image description here

enter image description here

2
  • Where is the splice going to be from the Romex to thwn ? the location with reguard to inside or outside the building? If your inspector would allow the Romex outside (mine would not, splice would need to be inside) a bushing is all that is required on the end of the pipe. Some use a threaded connector and add a screw on bushing. I would expect the splice made inside, then you would need to drill a larger hole so the threaded fitting would go through , dry fit everything to get your length right then glue , put the lock nut inside the box and if you are required to splice in the box.
    – Ed Beal
    Commented Apr 13, 2022 at 21:36
  • If your issue is that you are trying to make the clearance between the box and the LB short enough to keep the j-box in a thin wall then maybe you could use a metal LB and a close nipple. Also LB is subject to box fill calculation, most 3/4" LB's are to small for any xx/3 cable. Commented Apr 15, 2022 at 14:40

1 Answer 1

6

You can't run Romex there at all. Romex is only rated for indoor use. Conduit outdoors is a wet location. You could use UF-B cable, which is "outdoor Romex" if you will.

Metal boxes are great, but to come into one, you need a male PVC terminal adapter and a conduit lock-nut.

Now, there are 2 ways to use conduit. We'll talk about each.

Conduit merely as a damage shield for direct-use cable (or direct-burial cable).

In this case, you're using a Romex-like cable (NM, UF, SEU, SER) that is legal to directly use inside the walls. However, you reach a point where additional protection is needed (like for UF, the transition out of the house and down into the ground).

In that case, you're using a stick or two of conduit merely as a damage shield. It doesn't even need to be electrical conduit; any metal or sufficiently stiff plastic will do, doesn't even need to be pipe-like. People tend to choose electrical conduit because it's a safe bet.

In that case, you do not need a junction box where the conduit ends, you just need to de-burr the end of the pipe and make sure it exits where it won't create a problem for the cable (i.e. it needs to end in the middle of the wall, not pinned against the interior surface where a nail through the wall could harm it).

Also, you can disregard "conduit fill" rules, which means you can use #14 and #12 UF cables in 1/2" conduit (if you can get it in there lol, good luck!)

Conduit as a wiring method

In this case, you are using conduit as it was intended. You must start and end the conduit run in a junction box (or panel), but at that junction box you can transition to another wiring method. For instance, you might bring Romex to the junction box, then run THWN wires outdoors through the "conduit as a wiring method" then transition back to Romex in the other building's junction box.

However, in the conduit run, you must follow all the rules. Thermal derate (no more than 3-4 circuits per conduit), conduit fill, limits to bends, access points etc.

As far as conduit fill, it really works best to use individual wires such as THWN or XHHW. UF cable is at a huge disadvantage - it's a very wide and flat cable, so it requires very large conduit. 12/2 and 14/2 UF need 3/4" conduit. Larger UF needs ridiculously large conduit - 6/3 UF needs 2" conduit. Really. Two 6/3 UF's need 3-1/2" conduit!

Also, THHN and XHHW wires are actually allowed more amps for the same size wire. On a 50A circuit you can use #8 instead of #6, and that can pay for the conduit!