I'm replacing a few 2-prong receptacles in an old house, and all these outlets do not have ground wires. Cost for rewiring is too much and I'm thinking about using GFCI / AFCI receptacles instead.
My understanding is that normal 3-prong receptacles are not safe to use without ground wires, but how about GFCI ones? Also are there cases that I should use AFCI receptacles instead of GFCI ones?
    You know that dual function (AF+GF) receptacles are a thing, right? Also, what do you have for a panel? May 10, 2021 at 3:58
  • @ThreePhaseEel I didn't know actually. Googled it and found it might be a better choice. Thanks!
    – zlx
    May 10, 2021 at 5:00
TL;DR Install GFCI receptacles
Grounding, AFCI and GFCI perform three different, but complementary, functions.
Grounding takes care of a few different things, including providing a path for static electricity to get back to "ground" and enabling certain types of short circuits to complete in a way that will trip a circuit breaker. Grounding has been part of the basic design of residential wiring for a long time, but it is not critical when everything else works correctly. For grounding to work properly, it has to be installed in a particular way in the main panel and connected all the way to each device or receptacle.
AFCI protects against Arc Faults, which primarily means for protection. This includes certain types of problems that can be caused by loose wires, nails through wires, damaged insulation and other things. It is most effective when installed in (or near) the main panel so that it can protect against both wire damage and device problems.
GFCI protects against Ground Faults, which primarily means protection against serious injury and death. This is an imbalance between hot and neutral (or hot & hot on a 240V circuit). It is called "ground", but it actually does not require a ground connection to do its job. The key is that any electricity from hot that doesn't make its way to neutral must be going to someplace else. That someplace else is generically "ground" but may be: ground wire (ideal, safe), a person (not safe), a pet (not safe), exposed parts of equipment (not safe if they can be touched by a person), etc. The really great thing is that if the electricity would be going over a ground wire, but that ground wire doesn't exist, then it will go somewhere, and the GFCI will trip to stop that electricity.
The end result is that, in addition to its primary duty of protection against serious injury and death, a GFCI will effectively provide the protection that a ground wire would supply, even if the ground wire is not connected. So it is the cheap & easy way to convert from 2-wire to 3-wire receptacles. The way you do this is to install GFCI at the first receptacle in each chain, and any additional 2-wire receptacles can be replaced with 3-wire receptacles and marked as "GFCI protected, no ground". And you are safe.
In fact, you can install the GFCI protection in the breaker panel instead. That can be even easier to do, and less confusing (no need to figure out LINE vs. LOAD). Then you can replace all the 2-wire receptacles with 3-wire receptacles (and label them...). The catch is that generally speaking GFCI receptacles cost less than GFCI breakers and, depending on the type of panel and existing breakers, this may not be an option. GFCI receptacles are always an option.
  • The main argument against GFCI breakers is usually that it's much more of a pain to go to a breaker panel as it is often in an inconvenient location (and then there's the issue of everything being labeled correctly). With GFCI receptacles you are usually right there at the receptacle when it pops and it's quicker/easier to reset. Cost isn't too big a factor unless you're doing a whole floor/house.
    – TylerH
    May 10, 2021 at 18:16