I'm used to the gas furnaces, and I still want to swap out this 4 year old heat pump, but it would be too expensive. I recently bought a smart thermostat to try and help with the utility bills, but it requires a "C" or common wire. The thermostat did include a "C wire adapter" but it assumes that it is being used installed in a gas furnace with a control board. While looking at the system I noticed that it doesn't specify/label the 24v side or the 110/220 side. And as I REALLY do not want to experience another 220 flash. Can someone point me in the right direction?

enter image description here

1
  • Can you post photos of the actual thermostat wiring at the air handler please? Commented Dec 22, 2020 at 12:39

1 Answer 1

1

You don't have the C wire brought out to the thermostat.

See that COND UNIT CONTACTOR On the right is the Y wire going to the stat On the left is the C wire going to the transformer common. It is not labeled C but nevertheless it IS the C wire.

If you have more than 4 individual wires going to the stat then you would have an unused wire, you could connect that to the left terminal of the COND UNIT CONTACTOR and get your C wire brought out to the stat

Or you could run new stat wiring.

Or you could wire in the C wire adapter. Usually how those work is they take some of the signaling wires like G, W or Y wires, convert them into a multiplexed set on a single wire, then the thermostat breaks out the multiplexing internally. Then you repurpose the now-unused G W or Y wire to a C wire.

By the way if you live in a temperate climate then the heat pump isn't worse than a gas furnace. I'm like you, I am old-school with a central gas furnace and a central air conditioner. But I'm in a temperate climate and a lot of people around here run heat pumps and their costs are about equivalent to my combined electrical/gas.

Where heat pumps really suck (in my opinion) is cooler climates where you get a lot of snow and such in the winter and it's not that hot in the summer. Such as like Montana 50 years ago before Global Warming scotched everything.

1
  • See that COND UNIT CONTACTOR Actually, the image says "CONTRACTOR". But I am 99+% certain that CONTACTOR, as you spelled it in your answer, is correct, and that the manufacturer got it wrong. Could be that the engineers handed the drawing off to a graphic designer to make it look nice, and that designer had no idea what a CONTACTOR was and changed it to CONTRACTOR because "CONTRACTORS install these things." Commented Jan 21, 2021 at 14:57

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.