I'm looking at the cost of wire. A 500' spool of THHN costs roughly $75. I will need three of these to run hot/neutral/ground to outlets, etc. Three spools will cost $225. On the other hand, I can buy two 250' coils of cable and do the same work, but for only $125. Isn't cable just THHN wrapped into an outer sheath?
I'd much rather run THHN through my conduit than use cable (I understand cable cannot be used in conduit...well, it's cross-sectional area is too high to make it feasible), but the cost has me stumped.
Is there some technicality or spec that makes THHN superior to what comes in cable?
    Shop different. Home centers upcharge THHN quite a bit. Electrical supply, less so. One "technicality" is that it's actually marked, while "substantially the same wire" in cable is not.
    Commented Oct 27, 2020 at 20:45
  • @Ecnerwal The THHN was priced from an electrical supply store. That's part of what's confusing, I expected it to be a bit cheaper.
    – tnknepp
    Commented Oct 27, 2020 at 20:46
  • The wires inside romex aren't exactly the same as THHN -- in particular, THHN has a tough outer clear plastic coating around the main softer insulation, which makes it easier to pull through conduit without damage.
    – Nate S.
    Commented Oct 27, 2020 at 21:27
    There is on online cable and wire place you might price check against, but this site isnt about shopping....Also, check the gauges. my local big box depot is showing the three THNN a fraction cheaper than the 14/2 romex ($130/500 versus $140/500')
    – mark f
    Commented Oct 27, 2020 at 23:27
    A few electrical supply houses "stick it" to random walk-in consumers because they think they'll be "high maintenance". This is done by having a high "retail" price and a lower "customer account" price. I make clear to my suppliers that I'm price conscious and I get very good prices from most of them. City Electric, particularly. So if you dealt with a bad one, talk to others - and let on that you're sick of paying Home Depot prices... Commented Oct 28, 2020 at 4:27
4 Answers 4
All of these other answers primarily address the complexity of creating the wire, but cost really is due to a host of market forces such as base manufacturing cost (influenced by complexity of design and local labor wages), supply chain cost/availabilty, distribution costs, and economies of scale (how much of each wire type people buy and from where).
Don’t believe me? I encountered a situation at a big box store where a bare copper wire was more expensive than same gauge THHN wire: Is there a reason to prefer bare wire for Grounding Electrode Conductor?
THHN obviously requires far more processing than a bare copper conductor, so explain that one to me as something other than market forces.
Pricing is local, so things may be different in your area, and pricing has been all over the place in 2020. Supply has been short, and demand has been high, prices have been high, crazy high on some things.
But for today, right now on the Home Depot web site, just as a reference, 2x250' 12-2 Romex is $176.00, and 3x500' #12 THHN is $171.00.
They sell a lot more Romex, so you get that sheath pretty cheap.
https://www.homedepot.com/p/Southwire-250-ft-12-2-Solid-Romex-SIMpull-CU-NM-B-W-G-Wire-2-Pack-28828258/206647943
https://www.homedepot.com/p/Cerrowire-500-ft-12-1-Black-Stranded-THHN-Wire-112-3651J/202304641
Some places don't sell much THHN and don't pay much attention to their pricing. There are a lot of hardware stores don't sell conduit but have the same six rolls of THHN on the shelf for ten years, hoping someone someday will come through and not care / not notice the ridiculous price. In the meantime they sell a pallet of Romex every weekend.
Now if you're shopping at an electrical supply house - their pricing to the general public, not account holders, generally makes no sense at all. Pricing to electrical contractors, commercial / industrial / institutional customers, etc. with house accounts and negotiated pricing is totally different and makes sense occasionally.
Keep in mind if you're running metal conduit, you don't need a ground wire, so it's only 2 spools.
Also I think $125 is a great price for the Romex, but $75 is not a very good price for THHN. Could you be buying from a shop where Romex is a high-volume commodity, and THHN is an odd specialty?
You are certainly looking at fine-stranded (not 7-strand) THHN wire, which is more expensive to make and a great deal easier to work with - so apples and oranges.
Also, keep in mind the THHN is cross-labeled THWN-2. That means it can be run in wet locations. NM-B can never be run in wet locations because of the paper packing and the fact that it will damage the simple insulation on many manufacturer's NM-B.
Further, in wires large enough for 240.4(D) not to apply, you are allowed to run 75C thermal limits with THHN... so you can get 50A out of #8 instead of 40A... and 65A out of #6 instead of 55A.
  • Thanks Harper, helpful as usual. What do you mean by "wires large enough for 240.4(D) to not apply? I see nothing in that section that indicates I can use the 75C limit here. What I do see is 240.4(D)(5) specifies 12 AWG Copper limits overcurrent protection to 20A.
    – tnknepp
    Commented Oct 28, 2020 at 9:47
    It's exactly that 14, 12, and 10 ARE artificially limited in that section - but at #8 and fatter you get to follow the terminal ratings, which are commonly 75C for things that have terminals that large, rather than the 60C that NM cable is limited to.
    Commented Oct 28, 2020 at 12:43
-3
THHN ( Thermoplastic High Heat-resistant) isn't a brand name, it's a rating given by it's fire code. And indicates how long it takes to break down under load.
Where as Romex has a "protective" cover designed for pulling through a house. THHN is more for applications where a more strict fire code requirement exists or is warranted.
As far as your cost problem goes, I'd recommend calling your local codes office to explain the situation and ask them what's best. As for safety, electricity doesn't give second chances, better to be overly safe and expensive than cheap and dead.
  • I'm not really sure how this answers the question. Please feel free to take the tour to get a feel for the place, then browse the "how to answer" section of the help center to see what we expect in an answer. When you're done, go ahead an edit your answer to fit the standards. You've got the basis of a good answer in here, it just needs refining to be considered good here.
    Commented Oct 28, 2020 at 15:10
