I want to install 23 305w panels on my roof. It's a flat roof constructed with 2x8 beams spaced at 24". There is no snow load to consider and we get occasional wind and rain storms a few times per year.

Is this structure sufficient to support a solar array? I can space each panel a few feet apart. Each panel weighs 41lb with a psf of under 2.5.

2
  • What is the span of the 2x8’s?
    – Lee Sam
    Commented Sep 9, 2019 at 17:56
  • Up to 14' at the very widest span.
    – acpilot
    Commented Sep 9, 2019 at 17:57

1 Answer 1

2

2x8’s spanning 14’ can support between 31 psf and 53 psf depending on the species and grade of your 2x8’s.

Your existing flat roof “dead load” (load that does not change) is:

1) roofing between 3 psf and 8 psf depending on the type, number of re-roofs, etc.,

2) roof sheathing is between 1.5 and 2.5 psf,

3) roof joists of 2x8’s is 1.5 psf,

4) attic insulation (if any) is between 2 and 3 psf,

5) ceiling (if any) is between 3 and 4 psf,

6) miscellaneous, including lights, etc. is between 2 and 3 psf

Therefore, the total dead load is between 11.5 and 20.5 psf depending on all the materials on your roof. (Feel free to adjust my estimates depending on your exact materials.)

Generally, we add a “Live Load” (snow load, etc.) to the dead load to get a Total Load. However, you’ve indicated that there is no snow load.

Your 2x8’s spanning 14’ At 24” on center will easily support your solar collectors weighing about 2.5 psf.

So, the 2x8’s will hold them up, but we also worry about holding them down. If you live in a high wind area or seismic area, you’ll need to anchor the collectors to the roof too. Then, we worry about holding the 2x8’s to the bearing walls, then the bearing walls to the footings, etc.

Btw, solar collectors are the perfect shape to fly away...be careful.

2
  • We're in a major metro area so permitting is a big deal. Are you saying that this is still a hazard if using solar specific mounting hardware per approved mounting procedures?
    – acpilot
    Commented Sep 9, 2019 at 18:26
  • @acpilot If the mounting hardware is “site specific “ then no. That is to say, you may live in a hazardous zone, like Southern California for seismic activity or the Columbia River Gorge between Washington and Oregon that has high wind gusts.
    – Lee Sam
    Commented Sep 9, 2019 at 18:30