We're getting ready to build a detached garage/ADU about 100' from our main house, and have a quick question about getting power out to the building.

We currently have a 320amp service to the main house, with two 200amp panels (Siemens model S4080B1200A). Initially I wanted to use a 150amp plug on breaker and run 2/0 out to the garage, however looking at the sticker on the panel it looks like the max breaker size I can use is 100 amps.

However looking at the approved accessories for the panel, it lists Siemens ECLK2125 and ECLK2225 for subfeed lugs.

So looking at NEC 240.21 if I'm reading it correctly, I can use the sub feed lug kit to tap off my main panel, run power out the garage, and use a sub panel with a main breaker?

If i do it this way, do I need to size the wire for the 320 amp service coming to the house, or can I still use the wire sized for 150 amp?

My other option would be to use say two 75 amp circuits and two subpanels out in the garage/ADU. Id rather not do that as it will double up my costs for wire/conduit and panels but if using the sub feed lugs isn't an option, it seems like that may be my only bet.

Thanks!

3
  • When you say 2/0, are you referring to 2/0 copper or 2/0 aluminum wire? Where are you on this planet, and does your local jurisdiction ban aluminum wire? Commented Apr 27, 2019 at 16:39
  • 2/0 Aluminum, Seattle, WA
    – Chris
    Commented Apr 27, 2019 at 18:55
  • Welcome to Home Improvement! Good question; keep 'em coming! Commented Apr 27, 2019 at 19:42

3 Answers 3

3

Your panel's limit on stab ampacity only applies to double-stuff breakers

Your panel's label should read, among other things:

SUM OF QT BREAKER RATING IS NOT TO EXCEED 110A PER BRANCH CIRCUIT BUS STAB

Note here that it says "QT" breaker, while regular Siemens breakers are type QP. This is because this restriction only applies to Siemens tandem aka "double-stuff" or "cheater" breakers, which use a type QT label to distingush them from normal type QP breakers, or the type QNR double frame breakers that are used for breaker ratings above 125A.

As a result, I would go ahead and put the 150A type QNR breaker in the main panel in question, using 2/0 Al XHHW-2 for the hots and neutral with a 6AWG bare copper ground in 2" PVC conduit. (If you're stuck with copper because of local rules, 1AWG is the correct gauge, by the way.)

GO BIG OR GO HOME

For the panel in the ADU, we know two things:

  1. Spaces are cheap now compared to the cost of replacing a panel later because it filled up
  2. We need a main shutoff in the panel since we are dealing with powering a separate structure, but that main shutoff doesn't need to be a breaker (and can't be selectively coordinated with the feeder breaker in the main panel anyway!), just a switch

Given this, I would put a 42-space, 200A panel in the ADU and call it a day; if you don't mind losing a couple spaces, you could even use another S4080B1200A there, provided the panel is living indoors of course.

TORQUE ALL LUGS TO SPEC

There is one final thing to note here, and that is that you will need to use an inch-pound torque wrench or torque screwdriver to torque all loadcenter and circuit-breaker lugs to the torques specified on the labeling. This is required by the 2017 NEC in 110.14(D), and also is a good idea anyway, especially with aluminum wire, lest you want your subpanel install to be as reliable as Greg Biffle's infamous lugnuts.

4
  • Perfect thanks for the info that cleared it up. Just to make sure, this amazon.com/Siemens-QN2200R-200-Amp-240-Volt-Circuit/dp/… would be a good choice for the breaker at the main panel?
    – Chris
    Commented Apr 27, 2019 at 18:47
  • We chose this load center thd.co/2DBxoYC as it came with the surge protector, and had 60 spaces. I kind of went wild with me dream wiring diagram for the shop/ADU and only used 45 spaces. I dont have a problem up sizing to a 60 or 80 slot panel, but I was concerned with going to a 200A breaker downstream of my 200A main panels.
    – Chris
    Commented Apr 27, 2019 at 18:53
  • @Chris -- you'll want a QN2150R if you're using the 2/0 Al -- if you want 200A at the ADU, you'll have to go up to 4/0 Al with a QN2200R. Also, that's only a 30-space loadcenter you have there NOT a 60-space! The circuit count they give is meaningless and should be ignored!. Last but not least, there is absolutely no reason to be concerned about a 200A breaker downstream of a 200A panel if all it's doing is being a shutoff switch... Commented Apr 27, 2019 at 19:38
  • @Chris, yeah, "circuits" are completely false advertising these days. The vast majority of circuits need AFCI or GFCI, and those take a full space - that paneel will only support 30 of them. Your "60" relies on double-stuff breakers, which can't do AFCI or GFCI and went out of style with Pushmatic and MWBCs. They have value-packs like that in 40-space panels. If you want 60 or 80 spaces, just get a panel with thru lugs and jumper onward to the next panel. Commented Jan 20, 2020 at 21:39
0

You are making this way too difficult. Please, let's just start with what kind of load you would like to be able support in the new garage. Then we can figure out the best way to carry the load and the technicalities. PCL.

0

Your subfeed lugs will be downstream of a 200A breaker. So the wire run out to the garage will be protected by a 200A breaker.

"Oh, but it will also be protected by the small load since I'll never draw 200A". Not if your loads or wiring are misbehaving... That is why wire runs need to be protected by a breaker.

So you size your wires for 200A and you'll be good to go for tapping off the subfeed lugs. * You have a 200A feeder.

You don't need a main breaker at the outbuilding. You do need a shutoff switch/disconnect. Usually the cheapest way to get a disconnect is to use a service panel with a main breaker for your subpanel. When you do this, the subpanel rating and sub main breaker size do not matter and safety is protected in any case. Choose a panel which is appropriate for your needs. On this forum we're fond of LARGE panels (in number of spaces). They cost only a few dollars more at install time, but avoid the dreadful situation of running out of space.