I'm trying to install a humidity sensing switch for a bathroom fan that requires a neutral. There are two switches in the box, one for a light, one for the fan. There are 3 white wires (assuming they are neutrals) in the box twisted together. However, when I hook up the load, line, and pigtail to the neutral bundle, the switch doesn't work. Am I missing something? Every install video I've watched shows connecting it exactly as I have it, but mine won't work. I've tried 2 switches, just in case the switch was bad.

Update: Switch model is Leviton R02-IPHS5-0LW Switch Model http://www.homedepot.com/catalog/productImages/400/43/43ea781d-e83f-41d3-98c2-90fec341f3c6_400.jpg

Photos: switchbox wires switches connected

3
  • 1
    Can you post a photo of the inside of the switch box? Commented Aug 16, 2016 at 22:32
  • 1
    The model of the switch would also be helpful.
    – Ed Beal
    Commented Aug 16, 2016 at 22:57
  • added switch model and photos of wiring to post
    – Jenny
    Commented Aug 19, 2016 at 1:21

1 Answer 1

1

This one is simple -- you have the "line" and "load" terminals on the fan controller swapped, assuming the wire that is going to both the fan and the light switches is the line going in. The red screw (i.e. the screw on the same side as the silver neutral screw) is the load terminal, while there is a brass(?) screw on the opposite side of the device that is the line terminal -- they are also marked RD/WH/BK on the back of the device. Turn the circuit off at the breaker, and swap the two terminals -- you will need to swap the pigtail from the other switch over to the BK/brass screw on the device as well.

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.