Anything can go in anything. The differences come down to why something is going into something.
Individual wires (THHN/THWN) always have to go inside conduit. PVC Schedule 40 is sufficient above 8' indoors, buried underground, inside walls, etc. But if PVC Schedule 80 is required when subject to physical damage. That typically includes exposed inside a room (i.e., not hidden in walls) below 8' as well as certain places outdoors. For a typical run that means most of the conduit can be PVC 40 but very commonly some parts will need to be PVC 80.
On the other hand, non-metallic cables (a.k.a., Romex) never have to go inside conduit. However, when subject to physical damage they need to be protected. That does not need to be actual conduit - it can be anything that reasonably provides the protection. For example, you can use dimensional lumber or cut sections of plywood and screw the lumber or plywood in front of the cables to protect them from damage. However, if you want a ready-made solution then you can use any conduit which is rated for protection from physical damage, such as PVC 80. You can't use PVC 40 to protect cables from physical damage - it won't do any better than it does with individual wires. And when cable is not subject to physical damage it could be run inside PVC 40, but there is usually no reason then to use conduit at all.