I thought all I had to do to make an outlet switched was to break off the tab between the hot wires. Needless to say when I did that, the fan previously controlled by the switch quit working all together, as did other lights/outlets on the same circuit in another room. Is there something wrong with my wiring (or me)? Is this enough information?

1 Answer 1

18

No, just breaking the tab off is not enough. You need to have wiring specifically that goes from the switch to the outlet.

What likely happened is this: Most electricians will daisy-chain outlets, using one set of terminals for the feed, and one to go to the next outlet. By breaking off the tab, you removed power to everything downstream from that outlet.

Wiring for a switched outlet varies.


Sometimes there is a normal two-conductor wire that goes from the feed in the outlet to the switch (on black), and then the switch connects the two wires, and it comes back and goes to the top outlet (with the tab broken off). In this case the white wire should be colored red, or at least black to indicate it's hot. Red usually means switched. It's against code to leave a white wire carrying hot, but it does of course happen.

wiring with switch attached to outlet


The other way it's often done is by having the feed come into the switch, then carried over a 3-conductor wire to the first (switched) outlet, where the red wire is switched and is connected to the top outlet, white carries neutral, and black is hot and is both connected on the bottom outlet and daisy-chained along to the rest.

wiring with switch on feed side


There's other variations as well, though generally the power will be on the same circuit (breaker) - otherwise any fixture on it must have a clear indication that it is powered by two sources, and honestly I've never seen this done in a residential setting before (not even sure if residential code allows it).

So in short, you can't make a switched outlet unless the outlet is explicitly wired that way.

  • If you can re-wire (from an unfinished floor below), it's doable.
  • If you want to cut holes in the drywall and redo it, that works as well.
  • For a less intrusive option, you can put in some "smart" switches like Insteon, UBP, or X10 (though honestly, X10 has signal reliability problems, I'd stay away despite it being dirt cheap). Benefit of those is you don't even have to replace the outlet - once you have the switch in, you can put plug-in modules anywhere you want that will be controlled by that switch.

(Note: I prefer, and usually see -- at least in Canada -- the bottom outlet switched, but these diagrams show it as top switched, so I left my description that way)