2

I have a SquareD QO, 1 phase, 24 spaces, 34 circuits, 100A convertible main breaker, PoN, NEMA1, combo cover panel in my house as the main house panel. I had it installed by a licensed electrician over two years ago.

I had a friend tell me a horror story about his panel install so I took the panel cover off of mine just to inspect it. I saw there are 4 neutral bars on this panel, two bars high and two bars low. One of each on both sides. I noticed that he put all of the neutrals on the upper bars on both sides and the grounds on the lower bars on both sides.

Then I saw the grounding wire screwed in the lower bar on the ride side, the grounding wire goes outside to my grounding rod. It looks like he grounded it from the neutral bus that would go to a sub panel.

Should the neutrals and grounds be separated like that on the two different bars? And should there be a ground off the lower neutral bar to the grounding rod?

Part of me doesn’t think it’s correct, the reason why is this panel has 24 spaces, if the neutrals are on the two top bars and grounds on the lower two bars there isn’t enough room for 24 breakers?

Would I have to double up some of the neutrals and grounds or should there be one neutral and one ground together in one slot? I have read that you can put one neutral and one ground together only if it’s in the main panel.

enter image description here

enter image description here

enter image description here

11
  • 2
    Please upload a picture of your actual panel so we can see how things are actually wired. Commented Mar 5, 2023 at 4:24
  • 3
    Can you get us photos of the inside of your specific electrical panel installation please? Commented Mar 5, 2023 at 5:31
  • Those are (all four) neutral bars. Which ground can land on in a main panel. You could add accessory grounding bar kits if it would make you happy, but there's no need to. The holes for the proper kits are already there in the box.
    – Ecnerwal
    Commented Mar 5, 2023 at 14:15
  • 1
    What's up with the tape on the breakers? Commented Mar 5, 2023 at 14:21
  • Those breakers are empty, I purchased covers to put in those spaces. Just want them mark so I know which breaks have to come out. There is nothing to them and they are switched off.
    – Edward
    Commented Mar 5, 2023 at 17:51

3 Answers 3

2

The MAIN PANEL contains the first disconnect past the meter. The ground rod line must connect here (to the ground bar if they are separated). Also, here is the location of the neutral-ground equipotential bond tying neutrals and grounds together.

enter image description here

The panel you linked has four little NEUTRAL bars up high near the top of the panel. Your ACTUAL panel has three little NEUTRAl bars up high near the top of the panel. Note that all these are insulated from the panel chassis, that's what makes them neutral bars and not ground bars. So clearly your panel is NOT the one you linked. I suspect it is a 24/24 (i.e. allows zero tandem breakers).

If you had bars down low near the bottom of the panel, those would be optional, added GROUND bars. They would not be insulated from the chassis. Separating neutrals and grounds is a) mandatory in a subpanel. b) optional, but elegant and well-done in a main panel.

In a MAIN panel, grounds are allowed as guests on the neutral bar. Cheap builders rely on that a lot.

This panel can be configured either as a main panel or a subpanel.

I noticed that he put all of the neutrals on the upper bars on both sides and the grounds on the lower bars on both sides. Should the neutrals and grounds be separated like that on the two different bars?

On your panel, the "bars near the top of the panel" are staircased a little bit for easy wire entry. You seem to be calling that "upper" and "lower". That is wasted, they are all neutral bars. They are all insulated from the panel. Your panel according to your photo has no accessory ground bars. Feel free to add some. The panel labeling lists specific model numbers of ground bar designed to fit pre-drilled, pre-tapped sites all over the panel.

enter image description here

If this is a main panel, it doesn't matter. Separation is mandatory on a subpanel.

Note that in a main panel, you still have that neutral-ground equipotential bond.

And should there be a ground off the lower neutral bar to the grounding rod?

YES. The Grounding Electrode System (ground rod and connecting wires) connects to the GROUND bar if we're in a place where that matters.

Part of me doesn’t think it’s correct, the reason why is this panel has 24 spaces, if the neutrals are on the two top bars and grounds on the lower two bars there isn’t enough room for 24 breakers?

Well, given that you linked the wrong panel, I suspect your panel isn't actually a 24/34, it's a 24/24. There have to be enough neutral positions, or UL won't give the panel a UL Listing.

However, this is also a Plug-On Neutral (PON) panel designed to allow AFCI and GFCI breakers to pick up neutral by the vertical rails instead of taking a space on the neutral bar. Food for thought.

UL requires each neutral must be alone in its slot.

Would I have to double up some of the neutrals and grounds or should there be one neutral and one ground together in one slot?

NEC 408.21 [Neutral] Terminations. Each [neutral] shell terminate within the panelboard in an individual terminal that is not also used for another conductor.

However this has been a UL requirement for >50 years, just people weren't reading the instructions, so they had to put it into NEC.

Especially do not put the circuit's ground next to the neutral. If that had a connection problem, it could electrify all the grounds on the circuit!

However, GROUNDS are a different deal. Read the panel labeling, it often allows multiple grounds per slot.

I have read that you can put one neutral and one ground together only if it’s in the main panel.

Throw that book in the trash. It's horsepuckey. As you plainly see, neutrals must be alone.

Now it is true that grounds are allowed as guests on the neutral bar, but they share a spot, they can only share with other grounds, and to the limits specified in the panel labeling.

5
  • Thank you for taking the time to supply feedback. I added photos, im going to review your feedback.
    – Edward
    Commented Mar 5, 2023 at 13:55
  • So I uploaded pictures, I thought that was the link to my panel but my pics don’t look the same as the one in the link. I’m sorry about that. So I understand that each neutral bus must only have neutral wires in them, one neutral per slot. The ground can be a guest on the lower neutral bar, but not mixed. I’m checking the labels on my panel to see if I can do two or three grounds per space for this panel.
    – Edward
    Commented Mar 5, 2023 at 19:56
  • On my picture, it doesn’t appear that I have enough neutral and ground spaces for the number of potential breakers I can have in this panel. If more space is needed for grounds I could add an additional neutral bar to the panel and bind it to my ground neutral bar.
    – Edward
    Commented Mar 5, 2023 at 19:56
  • 1
    @Edward -- add ground bars first, and if your panel still doesn't have enough neutrals in it for the amount of circuits you have once all your grounding wires are moved to the grounding bars, then come back and ask another question. (QO panels have some oddities in this regard, but we'll need to know much more about your precise situation to help you if accessory grounding bars don't get you out of your jam) Commented Mar 6, 2023 at 0:29
  • Thank you and will do
    – Edward
    Commented Mar 6, 2023 at 0:57
1

Without a picture hard to tell for sure, but basically:

A typical panel will have separate ground and neutral bars. If it is the main panel then:

  • The neutral bars are grounded to the cabinet, usually with a clearly marked screw.
  • Grounds (whether branch circuits of the grounding rod wire) can be placed on the neutral bars but neutrals can't be placed on the ground bars.

While it depends on the specific panel, in general it is one wire per screw on the neutral bars but 2 or possibly even 3 (depending on the panel, depending on wire size) ground wires per screw on the ground bars.

In theory there should always be enough neutral and ground screws for every breaker (counting the 2 or 3 wires permitted per ground screw). However, there may be some panels with not-quite-enough screws, particularly if 1/2 size breakers are used (34 vs. 24). However, there are also usually some 240V breakers (e.g., water heater, HVAC, cooktop) that don't use a neutral at all or at least cut the number of neutrals needed down because they use one neutral for a double-breaker instead of two neutrals for two single breakers.

So it is quite possible that your panel may look a little strange but be 100% perfectly acceptable and code-compliant. But can't tell for sure without a picture.

1
  • 1
    Thank you for taking time out of your day to supply feedback. I added photos, im going to review your feedback as well.
    – Edward
    Commented Mar 5, 2023 at 13:56
0

OK here: While I agree with most of Manassehk said, I have to add that it's a good practice to put all the neutrals on their own bus bars, directly connected to the mains neutral, virtually eliminating the possibility of unbalanced neutral current flowing via the ground bars, even though they are electrically connected in a main panel. The other advantage is if the OP ever wants to install a whole house generator with a 200 amp transfer switch between the meter and the main panel, the main panel needs to get treated as a sub-panel, meaning the grounds and neutrals must be isolated (floating), having all the neutrals and grounds on separate bus bars would make that install a lot easier.

2
  • It isn't just good practice, it is required (as I included in my answer) to put the neutrals on the neutral bars. The optional part is whether to put grounds on separate ground bars on mix them in with the neutrals. As you stated, there are certain situations (generators, but also if you ever update outside and put in an outside disconnect) where not having grounds on the neutral bars is beneficial and will save future work. Commented Mar 5, 2023 at 6:16
  • And thank you for adding feedback. I’m on right now but going to review everyone that commented on this question when I get home later. I added photos.
    – Edward
    Commented Mar 5, 2023 at 13:57