My house has a 25 year-old dual-fuel split system heat pump. It seems to really go through contactors (the relay that turns on the compressor when the thermostat calls for heat or cooling).
The last one to fail lasted only about a year. I checked and there is solid 24vac on the coil. If I jiggle the contact with a non-conductive probe (e.g. a stick) it sparks and the compressor starts.
I had purchased what I thought was a sealed unit. But when I took off the cover (that covers the contacts-proper), there was crud in there. I also bought what is called a "one-and-a-half pole contactor), meaning it has line and load terminals for both phases (or 240vac) but one is always connected; I figure this roughly halves the probability of failure, over a two-pole one.
- How can I prevent this from happening so often?
- Should I get a contactor where the contacts are exposed, so I can clean them a couple of times per year?
- Is there a brand, or grade, of contactor meant for such problematic installations?
- Is the fact that I heat almost exclusively with wood, thereby minimizing the number of cycles of the contactor during the winter, a likely culprit?
FOLLOWUP: Based on the answers received thus far, it appears that the most likely culprit is that the contacts (in my recently-failed contactor) are not properly rated for controlling the motor load presented by the compressor. It appears that I need to be considering the IEC Utilization Category of a candidate contactor. These are described here: https://en.wikipedia.org/wiki/Utilization_categories Unfortunately, it is not clear what category is required by an HVAC compressor; AC-23 certainly would appear to fit the bill, but perhaps it is overkill and AC-3 or AC-4 would suffice. Additionally, none of the contactors I've checked online (Amazon has tons of them) actually specify their IEC utilization category. So I'm still somewhat at a loss.