0

DisconnectI want to use an interlock to have use of any breakers (if necessary) in my circuit panel.The problem is I have power from the utility meter feeding a service disconnect which, in turn, feeds the main lug breaker panel on the opposite wall of my garage. There is no "main" circuit breaker in the panel otherwise I would put an interlock kit there. I'm questioning whether I could place a "feed through" breaker panel in between the service disconnect and the main lug breaker panel. This feed through panel would have a main breaker and 50A breaker for the generator power and interlock kit as well as lugs to continue the main service to the breaker panel when not using generator power. Am I completely off base with this or does someone out there have some different ideas? Thank you

MLO Panel

9
  • You might find the cost of a feed through panel (meaning a panel with lugs on the busing to feed through) would likely be more expensive than replacing your MLO panel with a HOM4080M200 or a BRP40B200V25. Commented Oct 22, 2020 at 2:36
  • That could very well be. I was trying to utilize the main feed cable going across my garage. On the Eaton box you referenced what is the plug on neutral? Does that require different breakers. My current MLO box is a Cutler Hammer with BR type breakers
    – awac45
    Commented Oct 22, 2020 at 3:00
  • You can still use regular breakers. The point of the plug in is the plug in gfci and afci breakers don't have the inconvenient pigtail, and you just attach the line and neutral from the branch circuit to breaker. Commented Oct 22, 2020 at 3:12
  • I take it we're talking about an attached garage? Also, have you stepped back and considered what your loads actually are, and what you need for standby service and what you can live without? (Photos of your inside panel, especially if a directory label is available, would help tremendously here.) Last but not least, what make and model is your generator, or is that TBD? Commented Oct 22, 2020 at 3:32
  • If you want to use an interlock with this the interlock will have to be against the service disconnect.
    – Jasen
    Commented Oct 22, 2020 at 5:17

1 Answer 1

1

Edit because I can now see your pictures:

Best bet if it's a convertible panel

Call around to electrical supplies until you find an Eaton dealer. Give them your panel model number and ask them if it's convertible to main-breaker and if Eaton has a factory generator interlock for it. I have a feeling it's convertible because some features in the top area (like those funny pillars) don't make any sense otherwise.

Wow, that was super easy.

If it's NOT convertible, note the sticker "Use in Box G1 size (indoor) or G1R size (outdoor) panel". That refers to the steel enclosure (the thing 14" wide by 30" or so tall). Search for a panel that uses the same exact box as yours that is convertible - example, a BR4040N200R panel. Pull all the breakers and tuck them back, and remove the two fat hot wires. Then remove the screw now hiding under the bottom breaker and the screw between the pillars up top. There may be 1 or 2 more screws, and voilà, the bus assembly pops right out. Do the same to the breaker panel you just acquired, and swap the bus assemblies. Also swap lids. You have replaced your entire panel with astonishingly little work, because you picked exactly the right donor panel. Now you have a convertible panel; proceed as above.

The next best thing: Backfeed a breaker

Another option in this panel is to fit a 125A breaker in the top position of your panel, and backfeed that. (Sadly BR does not make a 200A plug-on breaker, and you can't use any other brand. So you'll lose a lot of usable ampacity.) You would remove the feed wires from the main lugs, and reroute to the backfed breaker. Then use a backfeed style interlock (BRPMIKBR) to interlock that with your generator breaker. Most likely these (4/0?) Al wires won't fit on the breaker so you'd need to change to 2/0 Cu.

If you can't make your panel convertible, use a transfer switch

That's your idea, and yeah, sure, I don't see any problem with that. You could use a main-lug panel and the kind of interlock kit where two "normal" breakers backfeed and are interlocked. One breaker is "Utility" and the other is "generator". Both backfeed the bus of that panel. Then off the main lugs of that panel, go onward to your large existing panel.

If you feel weird backfeeding and sending power "upward" through the main lugs, then mount the panel upside down so the main lugs exit the bottom. Then just pretend they're feed-thru lugs lol.

Edit: One big snag with this is your 200A service. That's an awful lot to backfeed into regular breakers simply because 200A regular breakers are scarce. What you need is a panel type that both a) supports 200A branch circuit breakers, and b) has an appropriate interlock. That's a scarce combination - for instance Square D's lowbrow HOMeline is deprived of many features, but it actually does have a 200A branch circuit breaker (HOM2200BB)... unfortunately not a factory interlock, so you'd have to go to the aftermarket.

Probably a better bet to go with any of the numerous of 200A main-breaker panels out there with 4-8 breaker spaces and feed-through lugs, such as the BR816N200RF. You could stick the generator breaker in one of the normal spaces and use a standard factory interlock, then feed the big panel off the "feed-through lugs". The only problem is, the boxes are gigantic (for cable bending space reasons).

Either way, the above boxes could actually stand in as a substitute for your current 200A main breaker/disconnect (that's kinda what they're for)... if you wanted to get into pulling the meter / pulling permits / inspection to get the power turned back on etc.

But if you're going with a gigantic panel anyway...

... just have a second main panel and call it good. Another 200A main breaker, this time panel right next to your existing panel, with interlock. It's fed with 200A wire either from your main breaker outside, or the panel next to it via double-lugs or "tee" Polaris connectors. Serving 200A wire to both panels is fine. This lets you take a clean-slate approach without having to move all your circuits. Simply move the circuits that you want on generator.

Or if you're moving circuits anyway... go with a smaller panel.

This lets you use a more compact subpanel such as a BRP20L125, with two backfed breakers interlocked. One backfed breaker comes from generator, the other from the large panel where it's fed from a breaker there. Then you move into this subpanel any circuits you want on generator.

2
  • Wow, thanks for all the info! I've got several leads to check out now. If I were to put a 200A main breaker panel in between the service disconnect and the MLO panel would it need to have an unbonded neutral? The service disconnect appears bonded while the MLO panel appears unbonded.
    – awac45
    Commented Oct 23, 2020 at 3:25
  • Yes, the service disconnect is your service point, the ONE place the neutral-ground bond occurs. Use metal conduit to connect panels, and that'll take care of your ground "wire" e.g. when you have 2 panels next to each other connect them with short conduit runs ("nipples") instead of cable. Metal conduit is a valid grounding path. Commented Oct 23, 2020 at 14:29